Thread: Diagnosing Daikin problem
-
18-08-2010, 06:21 AM #1
Diagnosing Daikin problem
FTXD50JVEA / RXD50JVEA.
Won't run. H6 fault code. No residual output current from compressor, which u would expect even if at fault.
Daikin say replace PCB, compressor and fan.
Is it possible to diagnose more accurately, as customer rightly points out, thats like your garage telling u to replace the engine, gearbox and wiring loom and that will fix your car. So would buying a new one.
Daikin adamant that all three components must be replaced, but interestingly customer had a similar problem just before the warranty expired, and only the PCB was replaced.
Any assistance / comments appreciated.
AJ
-
25-08-2010, 11:15 PM #2
Re: Diagnosing Daikin problem
I would go with a new unit which will offer 5 years warranty with not much more outlay..
-
26-08-2010, 10:34 AM #3
Re: Diagnosing Daikin problem
Replace the unit.
It's like $650 just for both outdoor PCBs. Not worth fixing daikin when they are out of warranty, parts are too pricey.
Get a panasonic if you want something more reliable, or a fujitsu if you care about cheap parts 5 yrs from now.
-
06-09-2010, 10:26 PM #4
Re: Diagnosing Daikin problem
Changing all parts seems like poor advice to me from a manufacturer. Compressor, fan and PCB can all be checked for correct operation.
The fan motor will be a simple resistance test, PCB can be checked for correct output, compressor can be judged easily enough. Download the manual and follow the steps for H6, im sure you will work it out.Last edited by Mentallist; 06-09-2010 at 10:31 PM.
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
problem with DAIKIN FCQ 71 > i need technical book
By mimifrigo in forum Air ConditioningReplies: 7Last Post: 13-01-2010, 03:06 PM -
DAIKIN problem
By mimifrigo in forum Air ConditioningReplies: 3Last Post: 05-01-2010, 09:02 PM -
Problem with an inverter compressor in V.R.V system DAIKIN R 407
By Harris Greece in forum Air ConditioningReplies: 10Last Post: 24-11-2007, 12:53 AM -
DAIKIN problem ?
By AaronX in forum Air ConditioningReplies: 11Last Post: 12-10-2007, 02:19 PM