    Finishing off vacuum - how to remove gauge?



    Hello

    Just finishing off my first install of a mini split. I've done everything by the book, and am currently sat at 300 microns vacuum with a digital gauge inbetween the service port and the manifold gauges.

    Just a bit confused as to how to finish off? I'm guessing the vac gauge won't like pressure too much, so i need to get it out before I release the refrigerant... how best to do it?

    Just pop the whole lot off now, and release the refrigerant unmonitored? But won't the vacuum be ruined when I release?

    Or, break it off, refit the manifold gauges and pump, and re-pump for a further half hour or so?

    Or, release refrigerant slowly up to a certain (low) pressure, then disconnect?

    Any advice appreciated.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Finishing off vacuum - how to remove gauge?

    Digital vacuum gauge is termocouple element and it is not afected with pressure in system. Release refrigerant until you see positive pressure at manifold gauges (cca 1barg) and then remove digital vacuum gauge.
    However, it is affected by oil in system and now is good time to clean it with alcohol.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,713
    Rep Power
    46

    Re: Finishing off vacuum - how to remove gauge?

    Alternatively next time use a 5 port manifold.
    Or one with these dual flare fittings.
    Where 1 has a schraeder fitting.
    Either way it is best to be able to remove the vacuum gauge, prior to system pressurisation.
    Grizzly

  4. #4
    Join Date
    Jul 2010
    Location
    UK
    Age
    54
    Posts
    47
    Rep Power
    0

    Re: Finishing off vacuum - how to remove gauge?

    Just to say thanks guys. Success.

Similar Threads

  1. Analog vacuum gauge
    By nike123 in forum Tools and Calculators
    Replies: 8
    Last Post: 23-07-2010, 06:05 AM
  2. Micron gauge and vac loss
    By lomb in forum Air Conditioning
    Replies: 22
    Last Post: 04-05-2010, 10:37 PM
  3. cps digital vacuum (torr) gauge
    By robin r33 gtr in forum Tools and Calculators
    Replies: 4
    Last Post: 09-04-2010, 05:27 PM
  4. cps vacuum gauge
    By cool_tech in forum Tools and Calculators
    Replies: 11
    Last Post: 03-07-2009, 01:18 AM
  5. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Replies: 7
    Last Post: 08-08-2008, 05:13 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •