    Copper pipe for Mitsubishi R410a Models



    Hi all.

    What grade of copper is needed for mitsubishi R410a models we have 4 MSH-GA60VB wall mounted units to fit on monday morning ..
    We have not used these units before with r410a refrigerant but after reading afew articles on the net i am a bit concerned that we have been supplied with soft copper 21swg by our supplier for the job.

    Will this stand the pressure ..

    Thanks chris..



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Copper pipe for Mitsubishi R410a Models

    just use normal fridge copper but use the concentric flare'er

    cheers

    richard

  3. #3
    tdmartin7's Avatar
    tdmartin7 Guest

    Re: Copper pipe for Mitsubishi R410a Models

    What is a CONCENTRIC flare tool? I called our local RSD and they are not sure, does it make a double wall?

  4. #4
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    70
    Posts
    604
    Rep Power
    18

    Re: Copper pipe for Mitsubishi R410a Models

    Quote Originally Posted by tdmartin7 View Post
    What is a CONCENTRIC flare tool? I called our local RSD and they are not sure, does it make a double wall?
    I think ECCENTRIC flaring tool is the correct name.
    It is not an equal cone, but is offset.
    The cone sweeps around as it flares and you end up with a very polished surface on the flare, and produces a much stronger flare.

  5. #5
    Join Date
    Feb 2007
    Location
    England
    Age
    68
    Posts
    9
    Rep Power
    0

    Re: Copper pipe for Mitsubishi R410a Models

    Normal fridge pipe is OK upto 3/4" however, check the charts in the HRP book to make sure the wall thickness is OK as you go up in size. I am using 16g on any thing over 3/4" if it's available.

  6. #6
    Join Date
    Jan 2008
    Location
    ptolemaida
    Age
    43
    Posts
    15
    Rep Power
    0

    Re: Copper pipe for Mitsubishi R410a Models

    hi chris i ve just entered re. i ve installated some of these{msz 60gb va} for example. your copper pipe is 5/8 and 1/4 .the thickness of your pipes must be 1.0mm for 5/8 and 0.8mm for 1/4. use a good eccentric flaring tool for not having leaks. {read carefully the installation manual and you wont have any problems!!!!