    Hi


    how would u calculate the heat load in a tank which has hydraulic oil and its temperature is to be brought down.

    will we use


    Q= mCpdT


    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: oil in tank heat load calculation

    Hi Ali,
    Whats the P stands for?
    What doe's the oil do and what is the entering temp and leaving desired temp?

    The flow, L/H is important too.

    Chemi

  3. #3
    Join Date
    Apr 2005
    Location
    Canada
    Age
    69
    Posts
    23
    Rep Power
    0

    Re: oil in tank heat load calculation

    Quote Originally Posted by abbasi
    Hi


    how would u calculate the heat load in a tank which has hydraulic oil and its temperature is to be brought down.

    will we use


    Q= mCpdT
    Use the formula if you are pumping the oil through a heat exchanger. It will allow you to calculate the load on the exchanger.
    Where:
    m is the mass flow rate through the exchanger in gpm, l/sec, etc.
    Cp is the specific heat of the oil. Usually about 40% of water
    dT is the temperature difference between the inlet and outlet of the oil through the exchanger.
    As long as all the units are compatible you should get good results.
    Another formula is Q= UAdT. This is used to calculate the heat transfer through the walls of the tank from the oil into the ambient (or out of the ambient into the oil). It works both ways. The trick here is to determine U.
    A is the surface area of the tank that is touching the oil.
    dT is the difference in the temperature between the ambient and the oil.
    The easiest way to do anything like this is to have the supplier of the exchanger do the calculations for you.

    Brian

  4. #4
    Join Date
    Jan 2003
    Location
    Venezuela
    Posts
    58
    Rep Power
    22

    Re: oil in tank heat load calculation

    Quote Originally Posted by abbasi
    Hi


    how would u calculate the heat load in a tank which has hydraulic oil and its temperature is to be brought down.

    will we use


    Q= mCpdT
    So why do you need to cool the oil down, or why is the oil getting to hot? Is it working in some extreme temperature conditions?

    Normally in a hydraulic system all the heat is coming from the pump, i.e., the electric motor.

    In normal working condition the energy the electric motor delivers will go into some work the hydraulic system performs, and only a small part will go into heating of the oil. However, when the system is idling, i.e., when no work is done, all the energy the motor delivers goes into heating of the oil.

    In bigger hydraulic systems, the pump will regulate so higher pressure means lower flow. The pump would also likely have an internal regulation to limit the flow when the pump is idling. So maybe the system is not adjusted correctly.

    Lets say the system is working correctly and still the oil is getting to hot. How do you plan to cool down the oil?

    Saludos,

    Jan

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: oil in tank heat load calculation

    On all the hydraulic systems we service - and there are at least 25 units - are mechanical cooling systems mounted.

    Mostly on metal working machines like lathes, milling machines...

    Also in cars and big farmer machines, you always find oil coolers.
    The transfomation from pressure to work is not a 100% conversion. The losses heats up the oil.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: oil in tank heat load calculation

    hmmmm

    Guys one of our team members here used bare tube Dx coil and temperature was to be lowered from 60 to 45 (F) and it worked. He maintains that Dx coil will do the job and it Did. What i studied was formulae I and then Binman also mentioned but how can this guy calculate w/out mass flow rate is it sheer experience or hit and trial may be both. coz he isnt very well qualified.

    Q=UAdt is more suitable but how to calculate U
    Last edited by abbasi; 13-06-2005 at 04:47 AM.
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: oil in tank heat load calculation

    It's like Cheme says: you can't calculate the heat load without a mass flow rate, unless you only need to cool the mass oil in a tank in a certain time and have a start and a stop temperature.
    Then you can submerge a DX coil. We serviced some time the German cooling units (DKW) of Trumpf lasercutting machines.
    They had a bare dx coil in it surrounded with a plastic pipe. Worked very well.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: oil in tank heat load calculation

    In plastic moulding injection machines, this is the method for cooling the oil, Not a DX but from a central cold water reservoir.

    No problems.

    Chemi

Similar Threads

  1. online heat load calculators
    By pradyumna in forum Tools and Calculators
    Replies: 3
    Last Post: 07-09-2010, 06:42 AM
  2. Calculating heat load
    By Abe in forum Technical Discussions
    Replies: 13
    Last Post: 13-08-2010, 05:40 PM
  3. Heat Load calculation for residential jobs
    By Herschmidt in forum Air Conditioning
    Replies: 2
    Last Post: 12-05-2008, 11:50 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Heat load calculation
    By Tony in forum Technical Discussions
    Replies: 3
    Last Post: 29-07-2002, 06:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •