    Liquid line temperature.



    A 4.H.P. Belcor split-system had the evaporator changed to Electra some time ago.The capillary (correctly sized) is on the condensing unit.The temperature of the returning liquid on a 20 foot run in 3/8" tube is neither hot nor cold, but the returning suction is "sweating" and at 78PSI with a head pressure of 300PSI at 45 Degrees C ambient. Normally you get a good "feel" for how a system is performing by the temperature of the suction and liquid lines.I have seen this a couple of times in the past but don't understand what causes it.There is no capillary tube in the evaporator.
    After changing the compressor and capillary the operating pressures are the same as is the temperature but the compressor does not cut out on klixon intermittently now even in the afternoon when ambient temperature peaks.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Liquid line temperature.

    Check your airflow (measure it).
    If you getting bigger diameter line colder than smaller one, you have restriction in evaporator or on bigger line. Maybe line is kinked somewhere or insulation particle is entered in pipe while it is hauled.
    Smaller diameter line should be at evaporation saturation temperature and bigger one should be at temperature of superheated vapor refrigerant.
    How did you charged your unit? By weight or other method?
    Could you measure both pipe temperatures and suction pressure?
    Last edited by nike123; 14-08-2010 at 07:15 AM.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Liquid line temperature.

    Hi romaurie,

    I have a thought, at such high ambient, not all the refrigerant condenses and some times you get vapour at the capillary inlet.

    This can cause the difrences in temp that you feel.

    And for our readers, Belkor is a local AC manufacturer.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  3. Low Pressure Cut-off switch on Liquid line
    By Vishnukurup in forum Air Conditioning
    Replies: 14
    Last Post: 03-12-2008, 09:34 AM
  4. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 01:43 PM
  5. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •