    I need to know the proper superheat for a walk in freezer with 404A refrigerant?



  2. #2
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: Superheat

    Quote Originally Posted by EricW View Post
    I need to know the proper superheat for a walk in freezer with 404A refrigerant?

    hi ericW,

    it depends on what point in the system you want to measure.

    - evaporator
    - compressor

  3. #3
    Join Date
    Aug 2008
    Location
    ireland
    Posts
    75
    Rep Power
    16

    Re: Superheat

    Hi,

    4 to 6 K superheat @ TEV bulb

  4. #4
    Join Date
    Nov 2009
    Location
    Poland
    Posts
    82
    Rep Power
    15

    Re: Superheat

    Superheat for the various ranges of evaporated
    6-8K for air conditioning
    8-10K for the cold
    10-13K for freezers
    4-6K has no such scope as the oil starts to less than 6K on tight foam which means a large number of factors in the oil.
    The gas is of no significance.

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. superheat ahd subcooling
    By jonc5553 in forum Fundamentals
    Replies: 3
    Last Post: 06-08-2010, 12:37 AM
  4. Replies: 12
    Last Post: 14-07-2008, 03:00 PM
  5. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •