Results 1 to 4 of 4
Thread: Superheat
-
13-08-2010, 02:07 PM #1
Superheat
I need to know the proper superheat for a walk in freezer with 404A refrigerant?
-
13-08-2010, 05:54 PM #2
-
13-08-2010, 08:08 PM #3
Re: Superheat
Hi,
4 to 6 K superheat @ TEV bulb
-
13-08-2010, 09:02 PM #4
Re: Superheat
Superheat for the various ranges of evaporated
6-8K for air conditioning
8-10K for the cold
10-13K for freezers
4-6K has no such scope as the oil starts to less than 6K on tight foam which means a large number of factors in the oil.
The gas is of no significance.