    Defrost problem.



    I have a -18 cold room.
    Problem is really interesting. when dfrost starting ( evrything stops and just resistanst (4) works. ) resistanst stars to turning in 4 sec stop 20 sec and turn again 20 sec. Why they start turn I realy don't understand. is it posible to magnatic area ?



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: Defrost problem.

    scorpx, understand -defrost
    not understand -resistant stars to turning in 4 sec stop 20 sec and turn again ?
    please repeat

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Defrost problem.

    Check the setting on the controller:

    what is the defrost stop temp?
    Where is the avaporator sensor connected to the fins?

    What controller do have?

    Details, details, details. Pictures are even better.

    The more we know - The more we can help.

  4. #4
    Join Date
    Oct 2009
    Location
    turkey
    Age
    39
    Posts
    45
    Rep Power
    0

    Re: Defrost problem.

    this is the evaporator spect


    Surface / Oberflache : 145,3
    Capacity /
    Nenn-Leistung (R 404 A) :38.800 W
    Air Flow / Luftmenge : 25.575
    Air Throw / Wurfweite : 25
    Coil
    Batterie 13x1650 13x1650 2x1650 4x150 300.0
    Evaporation : -8C


  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Defrost problem.

    It seems that a temperature sensor is too close to the heaters.

    Heat comes ON and the sensor opens, heater cools down and sensor closes.

    OR

    A wire/cable is loose somewhere breaking/making the circuit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Defrost problem.

    What's the end defrost temperature set-point. Put the bulb or probe (depending of type of thermostat you are using) far as possible of heaters on a fin location where is more difficult to defrost.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Oct 2009
    Location
    turkey
    Age
    39
    Posts
    45
    Rep Power
    0

    Re: Defrost problem.

    I think I counld not explain the main problem. Everything works fine, defrost is work great. problem is when "superheater - resistans - heater - hot plate" (I don't know english meaning of this part. Part that warm and melt the ice ) this part start turning in its own right. Because of that electric wires that connect the that part disconnect.

    Thanks for all posts...

  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: Defrost problem.

    So the defrost heater element turns on by itself even when not on defrost mode?
    And because of that you have had to disconnect the wires to it?

  9. #9
    Join Date
    Oct 2009
    Location
    turkey
    Age
    39
    Posts
    45
    Rep Power
    0

    Re: Defrost problem.

    So the defrost heater element turns on mean = spinning , rotate, circleing...

  10. #10
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: Defrost problem.

    I would hope a defrost heater element would be firmly attached to the evaporator and stationary!

    spinning, circling and rotating is what your car wheels do as you drive down the road.

    "turning" is a similar english word to spinning, circling, rotating, true; but "turning on" is really meaning "switching on" when taking about anything electrical.
    Sorry to confuse with technically incorrect terminology.
    Last edited by paul_h; 12-08-2010 at 11:24 AM.

  11. #11
    Join Date
    Oct 2009
    Location
    turkey
    Age
    39
    Posts
    45
    Rep Power
    0

    Re: Defrost problem.

    Quote Originally Posted by paul_h View Post
    I would hope a defrost heater element would be firmly attached to the evaporator and stationary!

    spinning, circling and rotating is what your car wheels do as you drive down the road.
    spinning, circling and rotating is what your car wheels do as you drive down the road. = absolutely Yes

  12. #12
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Defrost problem.

    hi
    i think ur problem came from contactor thermal device set too low&auto
    thats mean when the defrost starts the themal protector cuts off when it cools it cut in pls check the def contactor during defrost

  13. #13
    Join Date
    May 2007
    Location
    scotland
    Posts
    758
    Rep Power
    19

    Re: Defrost problem.

    could be a pump down system where defrost contactor only pulls in when unit switches of on the lp switch, check and make sure your solenoid isnt passing!

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. maytag fridge activation of new controller
    By jdrefrigeration in forum Domestic
    Replies: 5
    Last Post: 09-03-2010, 01:00 PM
  3. Trane HP Defrost Board Problem
    By FastEd in forum Heat Pumps
    Replies: 8
    Last Post: 05-09-2008, 01:30 AM
  4. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 09:22 AM
  5. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 07:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •