    hot liquid and suction lines



    probably an easy answer but i cant see why both the liquid and suction lines are hot.
    this is on a 9kw highwall split unit, air off 47 air on 20
    500psi on heat
    but not really performing well ,as in it doest kick up to high fan, and no its not oversized.

    any ideas



  2. #2
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: hot liquid and suction lines

    U sure your compressor is pumping?

  3. #3
    Join Date
    Feb 2009
    Location
    new zealand
    Posts
    5
    Rep Power
    0

    Re: hot liquid and suction lines

    yes hence 500psi

  4. #4
    Join Date
    Feb 2009
    Location
    new zealand
    Posts
    5
    Rep Power
    0

    Re: hot liquid and suction lines

    also sounds like is boiling in the indoor unit

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: hot liquid and suction lines

    Filters and coil clean? Fan blade/blower wheel clean?

    Where are you taking your temperature measurements? Just wondering as the interconecting pipe work will be hot during heating mode. I expect the liquid line is in fact an expansion line.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: hot liquid and suction lines

    500 psi sounds like you use air as refrigerant.

    Evacuate and recharge.

    Check that 4 way valve performs OK.

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: hot liquid and suction lines

    Quote Originally Posted by chemi-cool View Post
    500 psi sounds like you use air as refrigerant.

    Evacuate and recharge.

    Check that 4 way valve performs OK.
    Like Chemi says thats a high pressure, what refrigerant is it using? I hope the system is on R410A with pressures like that!

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hot liquid and suction lines

    Quote Originally Posted by djs View Post
    probably an easy answer but i cant see why both the liquid and suction lines are hot.
    this is on a 9kw highwall split unit, air off 47 air on 20
    500psi on heat
    but not really performing well ,as in it doest kick up to high fan, and no its not oversized.

    any ideas
    What is unit make and model? What is outdoor temperature?

    On high wall split system in heating mode both lines are part of condenser and therefore both should be hot.
    One hotter than another (one little below of compressor discharge temperature and other little below condenser saturation temperature).

    Recover and weigh charge. It is best to evaluate performance by observing temperature difference and air flow before recovery and evacuation.

    Δt of 27°C at indoor heat exchanger is sligtly high and could point to problem with insufficient air flow. Maybe fan speed is not on high, or filter and heat exchanger is dirty, or fan condenser is faulty, etc...

    If you have lines longer than unit is charged for, you need to calculate additional amount of refrigerant and see if it is added or not.
    Than charge correct amount and see if unit is performing OK by measuring air flow and air in and out temperature difference.
    Last edited by nike123; 10-08-2010 at 05:40 PM.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hot liquid and suction lines

    Quote Originally Posted by chemi-cool View Post
    500 psi sounds like you use air as refrigerant.

    Evacuate and recharge.

    Check that 4 way valve performs OK.
    Chemi, it could be R410a.
    500 PSI is 34.5 Bar which is 57°C CST which looks to me perfectly OK.

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: hot liquid and suction lines

    You can be on the right side, lets wait and see.

    Meanwhile you can enjoy the Chinese drivers....

    http://www.youtube.com/watch_popup?v=QESfEd180rQ

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hot liquid and suction lines

    Quote Originally Posted by chemi-cool View Post
    Meanwhile you can enjoy the Chinese drivers....
    At least they are driving pretty slow.

  12. #12
    Join Date
    Feb 2009
    Location
    new zealand
    Posts
    5
    Rep Power
    0

    Re: hot liquid and suction lines

    thanks for all replys ,it is on 410A so i expect around 500psi, the pipe is only 3mtrs so the supplied charge should be ok.
    imthinking i might move the themostat from the unit to the opposite wall.
    the unit is a mitsubishi ge80

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Liquid charging through the suction side
    By deu58 in forum Fundamentals
    Replies: 13
    Last Post: 02-07-2010, 05:23 AM
  3. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •