    R404A Pipe Size



    Dear friens

    I am design a coldroom Long 120 m L x 14 m wide x 12 m H
    Refrigerant 404A o 510
    Room Temp -28ºC
    Refrigeration Load 210 kw
    Evap temp –33ºC
    Suction Temp -35ºC
    I selected 12 evaporators 17,5 Kw each
    The diameter of suction pipe is more or less 150mm (6”)
    A 6” copper tube is very difficult to find locally
    I have the following alternative
    Use stainless steel pipe and weld with brach to copper
    What other alternatives could I have?
    Appreciate your comments
    Gwapa



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: R404A Pipe Size

    Stainless schedule 10 would be ideal, what about several smaller suction lines and header them in plant.
    Alternative is schedule 40 mild steel, should be API seamless A630... rated for low temp with WPL6 low temp bends and fittings etc., make sure that they are pickled/ cleaned before installed

  3. #3
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: R404A Pipe Size

    thanks Magoo
    4 tube 2 5/8" will be oK. I will conect three evaporators on each one.
    It is a spencer solution but thechnical featible

  4. #4
    Join Date
    Jun 2007
    Location
    Sri Lanka
    Posts
    88
    Rep Power
    0

    Re: R404A Pipe Size

    Dear Gwapa
    SS schedule 10 will be ok. But weld with a Tig (Argon Gas) welding machine. Did you take into account of the following when calculating the ref load of 210 Kw. 1) Refrigerant multiplier. 2) Evap fan heat load. 3) Defrost heater load. 3) Correction factor for SST. 4) RH vs KTD. 12x17.5 Kw = 210 Kw. If you have not accounted the above, the evaps are under capacity. Please make a note of it. This is for your info please.

  5. #5
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: R404A Pipe Size

    On 210 kW with R-404A, -35 deg C suction and 40 deg C condensing you would need 4 1/8" Suction Line, 1 5/8" Liquid Line, 2 1/8" Discharge Line.

    For each 17.5 kW evaporator coil, you would need 2 1/8" Suction and 5/8" Liquid Line.

    6" Suction line will upset the velocity. 4 1/8" Copper Tubing should be easy to get, as well as fittings/reducers.
    I am not always right, but I'm never wrong!

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: R404A Pipe Size

    Individual suction lines for each each evap in a common suction header will also lend a flexibilty should there be a drop on an evaporator . Oil management for compressor will be very critical during load variation/modulation.
    A microfiber oil separator will be needed .

Similar Threads

  1. Calculating weight of refrigerant based on pipe size
    By sheet59 in forum Air Conditioning
    Replies: 26
    Last Post: 21-10-2010, 09:07 AM
  2. Pipe size?
    By CRANK in forum Commercial
    Replies: 2
    Last Post: 28-06-2009, 08:54 AM
  3. Open expansion tank pipe size
    By A_Ahed in forum Air Conditioning
    Replies: 0
    Last Post: 18-04-2009, 01:14 PM
  4. extra length v pipe size v additional charge
    By misterfixit in forum Air Conditioning
    Replies: 18
    Last Post: 03-01-2007, 07:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •