    vilter compressor



    hi guys,

    i have a vilter compressor running on R22 for ice builder with 4 F suction temp and 112 F condensing temp. now the problem is worn out on the outer seat of the discharge valve. What do you think made this? any one can help?

    thank you



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: vilter compressor

    Is it a new system with a lot of steel pipe ?
    What model of Vilter & type of discharge valve ie ring type valve plate ?

  3. #3
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: vilter compressor

    vilter 450. the high suction safety head was already replace for R22 application. but still there's a problem on the worn out discharge valve

  4. #4
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: vilter compressor

    Quote Originally Posted by RANGER1 View Post
    Is it a new system with a lot of steel pipe ?
    What model of Vilter & type of discharge valve ie ring type valve plate ?

    no. its been running for 3 yrs. but they haven't solve the worn out problem.

  5. #5
    Waynexb's Avatar
    Waynexb Guest

    Re: vilter compressor

    we have had it where the discharge saftey spring had lost their tension alowing the discharge plate to bounce.is it an old machine

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: vilter compressor

    I have seen a case of the discharge valve rings actually wearing right through the valve plates .
    This was a R22 plant with Sabroe compressors .
    The plant was new & put it down to steel pipe dust,scale etc .
    Replaced once & all OK .
    Didn't seem to wear anything else but discharge valves .
    Maybe this happened to you .

  7. #7
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: vilter compressor

    hi ranger1,

    the worn out safety was already replace we are monitoring now the operating temperature/pressure hopefully we can find the root cause of the problem. because there are two ice builder. the ice builder 1 is running without problem for so many years on the ice builder 2 ( new one but total replica of the ice builder 1 ). that is why can't seem to understand what went wrong


    thank you

    lynark

  8. #8
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: vilter compressor

    Quote Originally Posted by lynark View Post
    hi ranger1,

    the worn out safety was already replace we are monitoring now the operating temperature/pressure hopefully we can find the root cause of the problem. because there are two ice builder. the ice builder 1 is running without problem for so many years on the ice builder 2 ( new one but total replica of the ice builder 1 ). that is why can't seem to understand what went wrong


    thank you

    lynark

    hi Ranger1,

    forgot to mention there are 3 compressor with 1 common suction header and liquid header.
    also got the running details.

    suction pressure: 21 psi
    discharge pressure: 255 psi
    ampere: 101

    suction pressure: 19 psi
    discharge pressure: 215 psi
    ampere: 96

    the design specs of ice builder are 4 F (27 psi ) suction and 112 F condensing temp.


    thank you

    lynark

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: vilter compressor

    Can you post picture of worn out discharge valve and/or a vilter part number .
    You also have 255 psi discharge on one compressor , is the an error .

  10. #10
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: vilter compressor

    Quote Originally Posted by RANGER1 View Post
    Can you post picture of worn out discharge valve and/or a vilter part number .
    You also have 255 psi discharge on one compressor , is the an error .

    hi ranger1,

    ok i'll try to pose some pictures. The outer ring of the safety head is the one being worn out. part number 517 of vilter parts

    But now the problem is got broken piston with lots of metal debris just open up the compressor yesterday to check the odd sounds its making. oil filter are full of black sludge so maybe the broken piston is due to lubrication failure but still checking the system.

    about the discharge pressure, 255 psi is correct that the highest recorded pressure the lowest is 215 psi they give me.


    thanks for the help


    lynark

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. copeland scroll durability
    By Third_techtrio in forum Technical Discussions
    Replies: 16
    Last Post: 23-01-2010, 04:47 AM
  3. Catastrophic compressor failure...need info
    By bsh3239 in forum Industrial Compressors
    Replies: 40
    Last Post: 28-11-2009, 04:30 PM
  4. Thumping noise in the compressor
    By Husky250 in forum Air Conditioning
    Replies: 6
    Last Post: 16-05-2008, 10:48 PM
  5. Compressor Capacity
    By engrkate in forum Fundamentals
    Replies: 15
    Last Post: 13-10-2006, 12:11 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •