Daikin Wall mount, flashy light, no worky
Got a small wall mount to look at tomorrow, about 3.5kw size. Infra red remote.
Apparently the green light flashes on the unit and thats about it!
I seem to remember there was a way to use the remote to get the wall mount to flash a fault code.
Anybody clues as to how to do this and what the various flashes flashes mean?
Failing that any daikin tech numbers you can recommend?
Cheers Jon
-
08-08-2010, 08:08 PM #2
Re: Daikin Wall mount, flashy light, no worky
Press the 'Mode' button and the Temp Up & Dn buttons at the same time until the dispaly reads 00
Then use the Temp up button to scroll through the first digit until the fan coil responds with the first code letter (different beep)
Use the Mode button to move across to the second 0 and repeat the Temp up button manouvre until the fan coil responds with the second fault code letter.
Text the fault code to 07797 801908 (Daikin Fault Line) for a quick explanation of the fault code
-
08-08-2010, 08:41 PM #3
Re: Daikin Wall mount, flashy light, no worky
Great! I'll give it a try tomorrow and see what i get!
Cheers Jon
-
08-08-2010, 08:47 PM #4
Re: Daikin Wall mount, flashy light, no worky
On the newer ones, hold the timer cancel button until it goes into fault code mode, then keep pushing the timer cancel button once at a time to scroll through all the codes, when you get a long beep, thats your code.
Probably just needs a power down reset if you get U4.
Andy
-
08-08-2010, 09:17 PM #5
Re: Daikin Wall mount, flashy light, no worky
Cheers Andy,
I'm not even sure how old the system is, we only get called every two years to service it as its in a private gym in a big country house, owners abroad half the time!
Cheers Jon
-
09-08-2010, 04:06 PM #6
Re: Daikin Wall mount, flashy light, no worky
Well i got a fault code of E7 which is a fault with the out door fan motor, went out side and this is what i found...
http://www.youtube.com/watch?v=w5xobceVgKw
Jon
-
09-08-2010, 04:23 PM #7
Re: Daikin Wall mount, flashy light, no worky
I'd have done me top button up to be sure though.
Health and safety first..........unless I'm in a hurry.
-
09-08-2010, 10:46 PM #8
-
10-08-2010, 07:37 PM #9
Re: Daikin Wall mount, flashy light, no worky
Did you sting them with a large bill?
Cheers,
Andy.Health and safety first..........unless I'm in a hurry.
Similar Threads
-
Condensate Heater For Wall Mount AC
By cool nirvana in forum Air ConditioningReplies: 7Last Post: 27-01-2010, 07:18 PM -
12.5 kw wall mount air con
By Andy W in forum Air ConditioningReplies: 18Last Post: 03-10-2009, 09:35 AM -
Daikin Ururu Sarara Wall mount
By sinewave in forum Air ConditioningReplies: 4Last Post: 19-03-2009, 09:15 AM -
How many forum posters does it take to change a light bulb....
By taz24 in forum Chit Chat & Service StoriesReplies: 7Last Post: 04-02-2008, 07:05 AM -
Daikin 5kW wall mounts.
By Temprite in forum Air ConditioningReplies: 2Last Post: 20-10-2006, 12:17 PM