Hi Guys,
31 degree's on Friday so i have spent the last 3 days travelling around resetting manual HP Switches. Whats the feeling in the trenches, Manual or Auto. The way i see it is:-
Manual: FOR:- As soon as the system goes HP it shuts down until someone physically goes to look and reset it.
Against:- As above, loads of calls
Auto: FOR, any temperary problem, high ambient ect will not shut the unit down permanently only until the pressure drops and then restarts
Against: If there is a genuine fault, Cond fan u/s for example the compressor will keep cutting in and out at high head pressure until it goes BANG !!!!!!
Personally, i think i would edge towards the auto switch but what are everbody elses feelings
Regards
Fatboy
-
31-05-2005, 01:01 AM #2
Re: HP Switches (Manual or Auto)
There is no question in Canada where we have laws that spell that out.
The code reads in part:
"...provide the compressor with protective devices that will automatically prevent the supply of energy to the prime mover of the compressor when an abnormal condition occurs during the compressor's operation, including,
(a) a high pressure limiting device in the compressor discharge line"
that
"(a) not be capable of automatically restarting the plant... and
maintain the visual warning until the abnormal or unsafe condition is rectified. O. Reg. 219/01, s. 39 (7)."
and that such controls
"... are independent of other control systems, are hard wired, regularly tested under operating conditions and calibrated as required..."
Brian Inman
-
31-05-2005, 06:51 PM #3
Re: HP Switches (Manual or Auto)
Hp switch cuts the system = problem . . . if it's atomatic , the problem will not go just by restarting automaticly the system , if that's the case waawwwwww (i like that , if the system fixes itself automaticlly) . . .
I'm against automatic switches although manual switchs cause us a load of phone calls it really protects the compressor . . . . so going to reset an hp switch and fix a little problem is more confortable than changing a compressor lololEngineering, sciences, math, physics and my brain will generate "not responding " soon
-
31-05-2005, 07:22 PM #4
Re: HP Switches (Manual or Auto)
Another question then - why do they make the switches with the choice of auto or manual ?
-
31-05-2005, 08:17 PM #5
Re: HP Switches (Manual or Auto)
From the simple reason that also here you get different opinions.
Personally/ I prefer the manual reset but always connect the warning red lamp to the high side.
Chemi
-
31-05-2005, 08:45 PM #6
Re: HP Switches (Manual or Auto)
Originally Posted by frank
-
31-05-2005, 11:31 PM #7
Re: HP Switches (Manual or Auto)
High pressure switches are not soley made for the fridge or a/c trade, hence the choice of manual/auto.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
01-06-2005, 10:27 AM #8
Re: HP Switches (Manual or Auto)
Originally Posted by frank
-
01-06-2005, 04:29 PM #9
Re: HP Switches (Manual or Auto)
Hi to all.
Here in Denmark we always use manual reset for high pressure, but
i do know of this problem. The cooling unit installed in the country
must always take acount to the ambient temperature, this means
that the SOT temperature for the unit is calculated to low.
SOT temperature = Safe operation temperature.
The problem is only caused for one thing ( $ )
Regards
Carlo Hansen
-
02-06-2005, 07:48 PM #10
Re: HP Switches (Manual or Auto)
Hi Guys,
I had noticed recently that all the new units coming from Hubbards all come with Manual Resets.
i just wish the designers would realise that the ambients in the uk do go over 30 degree's sometimes. It amazes me that even on refits costing hundreds of thousands of pounds that the condensers can't cope in a heat wave.
Regards
Fatboy
Similar Threads
-
MYCOM's manual
By ingherrera in forum New to REReplies: 14Last Post: 04-01-2010, 05:05 AM -
adsorption auto A/C?
By star882 in forum New TechnologiesReplies: 12Last Post: 11-11-2006, 11:16 PM -
Freeze Up Auto Or Manual In Chiller?
By abbasi in forum FundamentalsReplies: 9Last Post: 10-02-2006, 02:48 PM -
Toolbox manual
By nomiracle in forum Refrigeration BooksReplies: 1Last Post: 28-07-2005, 03:00 PM -
User Manual Scotsman Ice One AS/E
By JohnMac in forum Trouble ShootingReplies: 1Last Post: 09-07-2005, 11:17 AM