    HP Switches (Manual or Auto)



    Hi Guys,

    31 degree's on Friday so i have spent the last 3 days travelling around resetting manual HP Switches. Whats the feeling in the trenches, Manual or Auto. The way i see it is:-

    Manual: FOR:- As soon as the system goes HP it shuts down until someone physically goes to look and reset it.
    Against:- As above, loads of calls

    Auto: FOR, any temperary problem, high ambient ect will not shut the unit down permanently only until the pressure drops and then restarts
    Against: If there is a genuine fault, Cond fan u/s for example the compressor will keep cutting in and out at high head pressure until it goes BANG !!!!!!

    Personally, i think i would edge towards the auto switch but what are everbody elses feelings

    Regards

    Fatboy



  2. #2
    Join Date
    Apr 2005
    Location
    Canada
    Age
    69
    Posts
    23
    Rep Power
    0

    Re: HP Switches (Manual or Auto)

    There is no question in Canada where we have laws that spell that out.
    The code reads in part:
    "...provide the compressor with protective devices that will automatically prevent the supply of energy to the prime mover of the compressor when an abnormal condition occurs during the compressor's operation, including,
    (a) a high pressure limiting device in the compressor discharge line"
    that
    "(a) not be capable of automatically restarting the plant... and
    maintain the visual warning until the abnormal or unsafe condition is rectified. O. Reg. 219/01, s. 39 (7)."
    and that such controls
    "... are independent of other control systems, are hard wired, regularly tested under operating conditions and calibrated as required..."

    Brian Inman

  3. #3
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    861
    Rep Power
    21

    Cool Re: HP Switches (Manual or Auto)

    Hp switch cuts the system = problem . . . if it's atomatic , the problem will not go just by restarting automaticly the system , if that's the case waawwwwww (i like that , if the system fixes itself automaticlly) . . .
    I'm against automatic switches although manual switchs cause us a load of phone calls it really protects the compressor . . . . so going to reset an hp switch and fix a little problem is more confortable than changing a compressor lolol
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: HP Switches (Manual or Auto)

    Another question then - why do they make the switches with the choice of auto or manual ?

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: HP Switches (Manual or Auto)

    From the simple reason that also here you get different opinions.

    Personally/ I prefer the manual reset but always connect the warning red lamp to the high side.

    Chemi

  6. #6
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Re: HP Switches (Manual or Auto)

    Quote Originally Posted by frank
    Another question then - why do they make the switches with the choice of auto or manual ?
    To name one application,auto-reset is often used for cycling condenser fan/s.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: HP Switches (Manual or Auto)

    High pressure switches are not soley made for the fridge or a/c trade, hence the choice of manual/auto.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    May 2004
    Location
    england
    Age
    61
    Posts
    48
    Rep Power
    0

    Re: HP Switches (Manual or Auto)

    Quote Originally Posted by frank
    Another question then - why do they make the switches with the choice of auto or manual ?
    Hi Frank, auto hp switches are also required on some types of cascade systems, they are used on start up when the standing pressure of the low side refrigerant is high. cheers dill.

  9. #9
    Join Date
    Mar 2004
    Location
    Denmark
    Posts
    66
    Rep Power
    21

    Re: HP Switches (Manual or Auto)

    Hi to all.

    Here in Denmark we always use manual reset for high pressure, but
    i do know of this problem. The cooling unit installed in the country
    must always take acount to the ambient temperature, this means
    that the SOT temperature for the unit is calculated to low.

    SOT temperature = Safe operation temperature.

    The problem is only caused for one thing ( $ )

    Regards
    Carlo Hansen

  10. #10
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,171
    Rep Power
    25

    Re: HP Switches (Manual or Auto)

    Hi Guys,

    I had noticed recently that all the new units coming from Hubbards all come with Manual Resets.

    i just wish the designers would realise that the ambients in the uk do go over 30 degree's sometimes. It amazes me that even on refits costing hundreds of thousands of pounds that the condensers can't cope in a heat wave.

    Regards

    Fatboy

Similar Threads

  1. MYCOM's manual
    By ingherrera in forum New to RE
    Replies: 14
    Last Post: 04-01-2010, 06:05 AM
  2. adsorption auto A/C?
    By star882 in forum New Technologies
    Replies: 12
    Last Post: 12-11-2006, 12:16 AM
  3. Freeze Up Auto Or Manual In Chiller?
    By abbasi in forum Fundamentals
    Replies: 9
    Last Post: 10-02-2006, 03:48 PM
  4. Toolbox manual
    By nomiracle in forum Refrigeration Books
    Replies: 1
    Last Post: 28-07-2005, 03:00 PM
  5. User Manual Scotsman Ice One AS/E
    By JohnMac in forum Trouble Shooting
    Replies: 1
    Last Post: 09-07-2005, 11:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •