06-08-2010, 05:15 AM #1
Where does the refrigerant live when the system is off?
Say you have a 24,000 BTU/7kW PTAC
When the unit is off, where does most of refrigerant mass live?
-
06-08-2010, 06:29 AM #2
Re: Where does the refrigerant live when the system is off?
I have never heard of refrigerant being referred to as a Living component.
Where is goes to "sleep" depends upon the system design.
Usually the greater mass would be on the H.P. Side because as a medium it is in liquid form.
But then again there are flooded evap systems where the opposite prevails.
The refrigerant will naturally migrate to the low pressure side.
It really depends upon the system design as to where the bulk ends up!
Grizzly.
-
06-08-2010, 08:36 AM #3
Re: Where does the refrigerant live when the system is off?
Refrigerant will migrate to colder point > evaporator.
If the unit equipped with a TXV with MOP, some of it will be in the evaporator up to the rated pressure.
If a SV is in use, than over 95 % will be in the condenser and liquid receiver.
-
06-08-2010, 08:44 PM #4
Re: Where does the refrigerant live when the system is off?
-
06-08-2010, 09:07 PM #5
-
06-08-2010, 09:29 PM #6
Re: Where does the refrigerant live when the system is off?
Sorry my friend.
But Frank Has a point. Here in the UK and many other northern hemisphere countries.
In the winter the outside units ( Condenser / Condensing Unit) can become colder than the indoor ones.
Therefore these would be at a lower Pressure or Temperature (one and the same!).
In this situation guess where the refrigerant migrates?
So many factors dictate where the refrigerant ends up!
Surely to answer the original question where the bulk of the refrigerant lives.
could depend upon system design and the operating conditions?
GrizzlyLast edited by Grizzly; 06-08-2010 at 10:02 PM.
-
06-08-2010, 10:41 PM #7
Re: Where does the refrigerant live when the system is off?
Simple answer, included above, is that it will sit in the coldest place that it can get to.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
07-08-2010, 12:08 AM #8
Re: Where does the refrigerant live when the system is off?
Hi PWNED, chemi and frank are right in the example you've given, it is a different story for commercial and industrial applications though. OFF: switched off- cycled off?
-
07-08-2010, 01:03 AM #9
Re: Where does the refrigerant live when the system is off?
Well, I was asking where the bulk of refrigerant is stored, when the system is turned off, allowed to stabilize and temperature is fully equalized.
-
07-08-2010, 06:58 PM #10
-
07-08-2010, 10:37 PM #11
Re: Where does the refrigerant live when the system is off?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
08-08-2010, 06:12 PM #12
Re: Where does the refrigerant live when the system is off?
When a system is shut off, the refrigerant will try to "live" in the coldest point, the evaporator.
If the condenser is colder than the evaporator, the refrigerant will move to the condenser. The same applies when the compressor is cooler than the rest of the system.
If the entire system is at the same temperature, refrigerant will tend to "live" with the oil. Liquid will sit in the compressor!
Use crankcase heaters and good pumpdown with solenoid valve in the liquid line on off cycle.I am not always right, but I'm never wrong!
-
09-08-2010, 12:39 AM #13
Re: Where does the refrigerant live when the system is off?
Last edited by Brian_UK; 09-08-2010 at 10:02 PM.
-
09-08-2010, 10:02 PM #14
Similar Threads
-
Enthalpy Increasing Buffer System
By Reflexive in forum Technical SpeculationsReplies: 3Last Post: 23-12-2008, 03:18 PM -
Refrigeration system simulation and optimization
By autt in forum System OptimizationReplies: 7Last Post: 05-12-2008, 02:59 PM -
charging system with liquid refrigerant
By sidi in forum FundamentalsReplies: 12Last Post: 02-11-2008, 04:34 PM -
How an expansion tank works?
By Raadster in forum FundamentalsReplies: 6Last Post: 25-07-2008, 02:25 PM