    changing line set



    Is it mandatory to replace the line set if your replacing the a coil and condensor and going from r22 to r410a? I've heard conflicting answers. Thanks for the help!



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: changing line set

    If i was putting a system in for myself i would run a new line set, i would prefer to run a new line set on customers work too, but often they only look at the price.
    Is it mandatory? No, Is it advisable? Yes.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: changing line set

    Also depends on the quality of the existing pipework, is it suitable for the potential higher pressure?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: changing line set

    Quote Originally Posted by Brian_UK View Post
    Also depends on the quality of the existing pipework, is it suitable for the potential higher pressure?
    Hi Brian_UK,
    for R22 head pressures are abt 300 psig max.
    how high is it for R410 gas.
    Regards
    Kssoin

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: changing line set

    Kssoin, you can find this pressure in a log p/h chart of R410a, almost double.
    Will yu not change the compressors?
    If you perform after your job a pressure test on 1.1 x the max pressure your R410a system ever will see and it withstands this test pressure, well, then you can let your system run on the old pipework.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  3. About liuid line pressure drop.
    By wilsoncheung in forum Technical Speculations
    Replies: 15
    Last Post: 16-03-2009, 11:34 AM
  4. Coolpack help
    By marc5180 in forum Fundamentals
    Replies: 42
    Last Post: 31-01-2009, 10:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •