    Daewoo FRS2013 - Engineers Stumped



    This side by side F/F, triple thermostat, has developed a very mysterious fault that so far has beaten all of the engineers that have looked at it.

    Fridge side works perfectly. Compressor runs, fans run, temperature regulates etc etc.

    Freezer side: If select 'super freeze' (which lasts for 150mins), fan runs and freezer rapidly reached temp of -26C. After 'super freeze' finished, temperature in freezer slowly gets warmer (-2C within 2 hours) before fan starts running again, which then switches off at around -8C, even though freezer is temp set to -25C. Problem here is that door only needs to be opened two or three times before food starts to defrost!

    So far, engineers have replaced F sensor, D sensor, PCB Mainboard, dryer and cleaned and re-gassed, turned off for 72 hours etc - none of which has worked - and are now scratching their heads!

    Anyone out there any ideas? Also, does anyone know what the 'default' setting should be for the FRS2031 or how to enter diagnostic mode? The engineer manual (thanks Nike123) gives two methods of entering self diagnostics. The first (Lock on, Hold Freezer Set, Press Refrig Set 5 times) actually enters forced defrost mode and the second (Lock on, Hold Refrig Set, Press Lock 3 times) does nothing. Have found, however, that Lock on, Hold Refrig Set, Press Super Refrig 10 times and Lock on, Hold Sleep, Press Freezer Set 5 times, both give loads of engineer setable parameters but engineer manual doesn't cover what they are or what they should be.

    Any help would be much appreciated.

    Thx fmb



  2. #2
    Join Date
    Aug 2010
    Location
    UK
    Age
    58
    Posts
    5
    Rep Power
    0

    Daewoo FRS2011/2031 engineer codes

    Anyone have access to a working 2011 / 2031?

    I need to know what the default engineering settings are (accessed through buttons on front panel). These are not covered by the service manual and Daewoo tech doesn't know what they should be.

    Need to make sure a 2031 is set as it should be (eliminated virtually everything else!)

    Thanks

    FMB

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daewoo FRS2013 - Engineers Stumped

    A rise of 24° in 2 hours suggest a major insulation failure or a stuck defrost heater.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Engineers Huh?
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 19
    Last Post: 18-08-2011, 12:38 AM
  2. How many are actually 'qualified' to work on AC units (UK)??
    By Mr Memory in forum Air Conditioning
    Replies: 74
    Last Post: 28-05-2010, 09:36 AM
  3. refrigeration v's A/C Engineers
    By Latte in forum Chit Chat & Service Stories
    Replies: 20
    Last Post: 16-01-2007, 08:49 PM
  4. refrigeration engineers to strike?
    By dill in forum Chit Chat & Service Stories
    Replies: 7
    Last Post: 11-10-2004, 08:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •