  1. #1
    Sittard's Avatar
    Sittard Guest

    Lunite FH4540Z



    Hello All

    I would like to ask you for advice. I’ve got the Lunite single phase compressor equipped with terminal box with the 63Amps contactor. I would like to know if that contactor is sufficient to do the job.

    This is the electric specification:
    Rated Current RLA: 20A
    Max Current: 30A
    Start Current: 100A

    That starting current makes me a bit anxious.

    Many Thanks,
    Sittard



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Lunite FH4540Z

    No problem.

    Your 63amp contactor is sufficient to do the job.

    What you have to look at, is the MAX CURRANT.

    At start the contacts are closed and it takes less than a second for the compressor to run and drop the amps.

    When you disconnect the contactor at high currant, there is a big spark between the contacts and that is what kills contactors.

  3. #3
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Lunite FH4540Z

    i have seen 10 hp 3 phase compressors on 32 amp contactors, your little pot will be fine!

  4. #4
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Lunite FH4540Z

    http://www.actrol.com.au/PriceGuide/..._Section_4.pdf

    according to the above link fla are 7 amps

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Lunite FH4540Z

    Many contactors have the max motor hp/kw marked on them or on a chart on the box come in. I think your compressor is a 3hp model.

Similar Threads

  1. l'unite hermetique
    By Andy AC in forum Commercial
    Replies: 4
    Last Post: 12-06-2009, 07:52 PM
  2. l'unite hermetique R12 Condensing unit
    By airefresco in forum Commercial
    Replies: 13
    Last Post: 08-02-2008, 09:08 PM
  3. Qualitair / L'unite compressor problem
    By wotsie in forum Trouble Shooting
    Replies: 8
    Last Post: 10-11-2007, 04:50 AM
  4. L'Unite hermetique wiring
    By Chilly willy in forum Electrical
    Replies: 11
    Last Post: 20-08-2007, 06:38 AM
  5. L'Unite Hermetique compressor
    By iceman007 in forum Commercial
    Replies: 4
    Last Post: 27-06-2004, 08:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •