    Have a U5 fault keep coming up. strange thing is it runs up fine in the morning runs as normal then certain times when i look at the intellegent controller it says U5 fault on 3units thers about 30 units on this intellegen controller then theres a wall mount controller that controls the 3 units. If it was the PCB surely the fault would come up straight away and the unit wouldnt run? Could some one give me advice and do you think it is the PCB? i have to go back to the job out of hours and want to know what im looking for. Cheers
    Dec 2008
    563
    Re: U5 Fault Daikin VRV ll
    Sounds as if it might be a fault on the control circuit between the three units units and the wall mounted controller. Check for a loose connection or it could be a setting error on the remote controller.
    Dec 2006
    Aust
    68
    Check P1 p2 wiring loop for loose connection.
    Test for break or short in cable.
    If you have more than one controller on site swap them around and see if the fault transfers to the other unit. This will test the controller.
    Make sure controller cable is away from current carrying cables (Noise interference).
    No longer Active
    Aug 2009
    Dartford
    88
    cheers guys. Am i right in thinking its deffinatly not the PCB?
  1. Daikin VRV U4 FAULT
    By leegally1983 in forum Air Conditioning
    Last Post: 30-11-2010, 11:49 PM
  2. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Last Post: 28-07-2009, 01:26 AM
  3. Daikin Split f3 Fault
    By moondawn in forum Air Conditioning
    Last Post: 01-06-2009, 07:09 PM
  4. Daikin Cassette Fault
    By symon22 in forum Air Conditioning
    Last Post: 23-05-2008, 06:19 PM
  5. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Last Post: 05-02-2007, 02:41 AM