Results 1 to 7 of 7
  1. #1
    Grover-1's Avatar
    Grover-1 Guest

    Low oil pressure alarm - very intermittent



    I have a Carrier Ultima 53 with about 8,000 hours on it. It runs and cools fine except once or twice a week it will set an alarm. The alarm is for low oil pressure. Oil level is fine and recently changed. Bad sensor? Any other ideas? Seems it would either have low oil pressure or not - not just once or twice a week. Thanks!!



  2. #2
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    193
    Rep Power
    20

    Re: Low oil pressure alarm - very intermittent

    what is the average oil pressure? does it dip after defrost or on pump down. does it only get loaded once per week. is there any commonality to the tripping time?

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Low oil pressure alarm - very intermittent

    You could be running at too lower loads for too long or slightly SOG. Check for oil logging and SH.

  4. #4
    Join Date
    Jul 2010
    Location
    England
    Age
    64
    Posts
    8
    Rep Power
    0

    Re: Low oil pressure alarm - very intermittent

    A possibilty is refrigerant migrating into the oil when the compressor is idle.?
    On start up the oil could possible foam?

    Steve

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Low oil pressure alarm - very intermittent

    Quote Originally Posted by Old cooler View Post
    A possibilty is refrigerant migrating into the oil when the compressor is idle.?
    On start up the oil could possible foam?

    Steve
    I also agree with Old cooler. Many could be the reasons for that happen.

    Check if your cranckcase heater is operating during the idle.
    Also see if the compressor don't start immediatly with 100% of capacity. Start at minimum capacity for a while.
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Low oil pressure alarm - very intermittent

    Check the oil pressure with your gauges to be sure of the pressure.

    Check the oil filter as well, if the unit wasn't cleaned well at the factory, it could well be the reason.

  7. #7
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: Low oil pressure alarm - very intermittent

    because it a problem only once or twice a week .... i would look at the time of the alarm v's load.... flood back etc etc ...have u an oil seperator on it???(not familiar with that unit)

Similar Threads

  1. Carrier Genesis AL2 High Pressure alarm.
    By Jim Crooks in forum Transport
    Replies: 7
    Last Post: 02-11-2009, 03:58 PM
  2. Effect of inverter on Pressure Ratio
    By GIB in forum Air Conditioning
    Replies: 6
    Last Post: 03-10-2009, 01:54 PM
  3. High Deferential Oil Pressure Alarm
    By NNNNNN in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2007, 01:06 PM
  4. Replies: 27
    Last Post: 27-10-2006, 03:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •