    operating pressure screw r717



    Why is the opearting pressure only half of the discharge pressure on one compressor and they r about the same on the other?Need help !!



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: operating pressure screw r717

    Quote Originally Posted by stanthonycold View Post
    Why is the opearting pressure only half of the discharge pressure on one compressor and they r about the same on the other?Need help !!
    At what stage of loading are each of the compressors?
    Unless they are both fully loaded, comparison is irrelevant!
    If they are both fully loaded then you could have loading issues with the Higher pressure one?

    There is not enough info to guess further!
    Grizzly

  3. #3
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: operating pressure screw r717

    Quote Originally Posted by Grizzly View Post
    At what stage of loading are each of the compressors?
    Unless they are both fully loaded, comparison is irrelevant!
    If they are both fully loaded then you could have loading issues with the Higher pressure one?

    There is not enough info to guess further!
    Grizzly
    the one with 70 psi operating pressure and 130 psi discharge pressure is at 100% while the compressor that seems to be running fine is at 80% with operating pressure of 125 psi and discharge pressure of 125-130 psi..

  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: operating pressure screw r717

    Quote Originally Posted by stanthonycold View Post
    the one with 70 psi operating pressure and 130 psi discharge pressure is at 100% while the compressor that seems to be running fine is at 80% with operating pressure of 125 psi and discharge pressure of 125-130 psi..
    There are suction, discharge and intermediate pressures? All of them are operating pressures. What is your meaning of operating pressure?

Similar Threads

  1. what is useful of Economizer?
    By Ahmed.ragab in forum Industrial Compressors
    Replies: 33
    Last Post: 18-08-2010, 12:15 PM
  2. PT chart for different elevations
    By dkalasz in forum Tools and Calculators
    Replies: 84
    Last Post: 20-07-2008, 05:09 PM
  3. carrier screw chiller
    By moideen in forum Air Conditioning
    Replies: 4
    Last Post: 10-05-2008, 08:24 PM
  4. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Replies: 13
    Last Post: 12-08-2006, 10:27 PM
  5. screw compressor
    By vinod in forum Trouble Shooting
    Replies: 9
    Last Post: 17-12-2005, 01:46 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •