Results 1 to 21 of 21
Thread: hydrocarbons
  1. #1
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21
    Thumbs up hydrocarbons
    Hey all
    Could anyone tell me how the law stands on reclaimation of HC refrigerants like R260, R600 and the care ranges.
    Because they have no ODP hazard are the regulations as strict.
    Also when reclaiming these refrigerants what is the best reclaim machine to use.
    Thanks
    Neil
  2. #2
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21
    Re: hydrocarbons
    "In this final rule, the EPA has determined that second generation replacements, if they are non-ozone depleting and are replacing non-ozone depleting first generation alternatives, are exempt from reporting requirements under Section 612"
    from : http://www.autocool-refrigerants.com...osafe_tech.htm
    Engineering, sciences, math, physics and my brain will generate "not responding " soon
  3. #3
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21
    Re: hydrocarbons
    Hi all.
    Because the company has just put an order in for the R290 refrigerant I am looking for any litigation I could show the tech director of the company. Because if I can't he will ask me to vent it to atomosphere and I already have 26 units waiting for new R290 compressors, apart from the Health and Saftey factors that the refrigerant is heathier than air which makes it an asphixiant, also it means I will be letting a flammable gas into atomosphere, were I use oxy/acette brazing equipment. He says that I cannot produce a valid reason for the company to fork out £600 on a new reclaim unit that can work with H.C refrigerants.
    neil
    If you can't see it, it can't hurt you.
  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Re: hydrocarbons
    Sorry Botrous, a mix-up in terminology here.
    The EPA (Environmental; Protection Agency) is an American enforcement agency that has no jurisdiction in the UK (or Europe for that matter).
    Neil, in the UK here are some pointers.
    In the UK the similarly sounding, but completely different, EPA (Environmental Protection Act ? 1990) http://www.opsi.gov.uk/acts/acts1990..._en_1.htm#tcon is the legal instrument that will govern the vent to atmosphere of refrigerants. The best place to start is section 33.
    If you are prosecuted for illegal venting of anything, it will be by the Environment Agency, http://www.environment-agency.gov.uk/ unless you are unfortunate enough to injure or kill someone in which case it will be the HSE (Health & Safety Executive). http://www.hse.gov.uk/
    Needless to say it is a very grey area, because having a GWP below 15, HCs are perceived to pose no distinct threat to the environment. The rules surrounding their retrieval are blurred.
    You can gain valuable insights from CARE themselves, https://pgw100.portal.gases.boc.com/...gin=pgwspecial and the Institute of Refrigeration http://www.ior.org.uk/ and ACRIB, (Air Conditioning and Refrigeration Industry Board) http://www.acrib.org.uk/ that both have guidelines on their safe use.
    ________
    medical marijuana strains
  5. #5
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21
    Re: hydrocarbons
    Thanks Argus
    After coming of RE last night I did find a little information on the ACRIB site. But the regulations concerning H.C refrigerants is a bit bleek to say the least. I think that I might join the IOR I have a membership form around here somewhere, see what their tech notes say.
    Neil
  6. #6
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Re: hydrocarbons
    Neil,
    You may also talk to BOC / Dupont who have recently acquired the distribution of CARE products in the UK. John Rodriguez, who posts here sometimes works for BOC, and may be able to help you from a supplier?s point of view. I believe that they have user guidelines for HCs.
    Since yesterday I have also had a look at EN 378. It?s worth reading Part 1 where L1 group refrigerants (flammable gases) are prohibited in use in direct A/C systems used for human occupancy. There are safety indicators in this standard.
    If your firm is going to handle it, I suggest that it is prudent to survey the competencies of handlers and to draw up a health and safety risk assessment for the transport, storage and use of HCs. Your supplier will give you H&S data sheets (MSD Sheets) that you can give to your operatives and keep on file.
    Check also that your premises are suitable for storage, fire protection is adequate and your building insurance and public liability insurance is suitable.
    All best
    Argus
    ________
    volcano vaporizer
  7. #7
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    51
    Posts
    135
    Rep Power
    19
    Re: hydrocarbons
    I'll ask one of our guys who makes it his business to keep up on legislation. Not something I know about, but venting HCs isn't exactly safe, a lot of customers have it flared off where they have the facility on site, not sure about those that don't or where you are in an enclosed space.
    It's a lovely day to pump some gas
  8. #8
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Re: hydrocarbons
    Quote Originally Posted by Johnny Rod
    .......venting HCs isn't exactly safe, a lot of customers have it flared off where they have the facility on site, not sure about those that don't or where you are in an enclosed space.
    Thanks, John
    The issue of HC disposal is a grey area that needs some thought. Not something I'm too well up on either. The situation is clear for conventional refrigerants, but not specific for HCs.
    Obviously it is unsafe to do anything like venting near cellars, underground areas etc.
    The UK laws on hazardous waste changed this year.
    All refrigerants are hazardous waste under the new regulations that came out this year. Section 1 - 14 in the Waste List itemises the CFCs , HCFCs, HFCs etc and solvents, but is not specific about HCs. (Are HCs classed as Halogenated Solvents? - if so then are covered.)
    There is a schedule in the waste regulations that lists properties that would render substances hazardous and HCs would certainly fit in.
    Waste oil is always a hazardous waste.
    The point I?m making is that Neil?s legal duty of care (or anyone else?s for that matter) extends to safe and responsible disposal as well as safe use.
    ________
    vaporizer answer
  9. #9
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    51
    Posts
    135
    Rep Power
    19
    Re: hydrocarbons
    Hydrocarbons aren't halogenated but I am sure they will be covered under one of the sections - typically our waste guy has gone home about half an hour ago so will ask him next week.
    A blanket for everything really is that operations should be risk-assessed, which includes the materials and the way in which they are used. Until that's done...
    Will be back with the answers next week.
  10. #10
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Re: hydrocarbons
    Thanks - I didn't know that. Informative as ever. What is a definition of Halogenated gases? I thought that it was a compound containing Hydrogen? I should have paid more attention in school!
    HCs as a refrigerant are not specifically mentioned in the Waste List, but there is a schedule of hazard properties in the Waste Regulations that would fit.
    The main problem with handling the stuff as a waste regularly is the notification of premises and staying below the 200kg annual limit.
    ....our waste guy has gone home about half an hour ago so will ask him next week.
    Anyone would think it's a Friday.....
    Couldn't agree more. I think that a risk and competence assessment is part of the employer's obligations under the H&S at Work Act.
    It would be unwise not to.
    ________
    buy glass pipes
  11. #11
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21
    Re: hydrocarbons
    Due to my employer making me redundant today ,because of lack of work.
    Plus the way the company is run. They still have a few kilo's of R12 which I had been pestering for them to get rid of since I had been there (nearly four years), and it took the company two years for them to rent a reclaim bottle for me. So they also have a lot of old bottles full of spent refrigerant, that I had to reclaim in.
    So I think in the end the R290 refrigerant will probably be vented to atomosphere.
    Neil
  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51
    Re: hydrocarbons
    No doubt your local Environmental Health Officer would be interested in this fact
  13. #13
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21
    Re: hydrocarbons
    Hi Frank.
    I need a reference first.
    Neil
  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Re: hydrocarbons
    Quote Originally Posted by neil sailes
    ...I need a reference first....
    No I don't think so Neil, as you have been made redundant there shouldn't any comebacks on you for reporting a potential problem to the Environmental people.
    You could always do the call as a "concerned individual".
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  15. #15
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Re: hydrocarbons
    It's the Environment Agency who will do the inspections.
    http://www.environment-agency.gov.uk/subjects/waste/
    Local contact points are at the bottom of the page.
    Any CFC, R12, R11 R502 stored, but not in use in systems in the UK, is considered waste. Since July this year, all refrigerant waste is termed Hazardous Waste and requires licenses and notification of premises where it is held or stored.
    Pain in the neck, I know, but it?s the law in this country.
    Venting this stuff is just like fly-tipping ? they hate it.
    Your ex-firm is probably in breach of something??
    ________
    Suzuki TSX history
  16. #16
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    51
    Posts
    135
    Rep Power
    19
    Re: hydrocarbons
    Seems to be a bit of a grey area this one, not a definite answer yet.
    In reply to Argus, halogenated materials contain chlorine, fluorine, bromine and/or iodine. I don't know of any refrigerants with iodine in them, Halons contain some bromine, and we know the rest about CFC/HCFC/HFC/FCs. Apart from the ozone-depletion problem, incinerating these materials at too low a temperature gives rise to dioxins which are very toxic (e.g. Agent Orange was a dioxin), which is why burning PVC is a bad idea, and why it costs a lot to dispose of old refrigerant.
    Like Argus says, new regs mean a lot more material is now classed as hazardous, but I think there are probably still lots of firms that have yet to apply for their new documents under the new rules.
  17. #17
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Re: hydrocarbons
    Thanks for the reply, John.
    Chemistry is not my long suit, so to speak, so that was very helpful.
    If your colleague has any insights into the safe and legal (in the UK) disposal of HCs, I would be grateful to hear them.
    There are a number of alternatives I can think of;
    1. Vent them off. Not a good idea in my opinion as they have a habit of collecting in still atmospheres at low level. Additionally, what do you do with the oil? Unsafe and unsound.
    2. Flare them off. Again, consider the oil, unless you can arrange to atomise it in the flare. To do this safely you will need the equipment to do it, somewhere designated to do so and a fire safety policy ? I don?t think you can let a sheet of flame go from the edge of the roof or in your firm?s yard.
    3. High temperature incineration?
    ________
    buy air one vaporizer
  18. #18
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21
    Re: hydrocarbons
    Hi Argus.
    I think I will contact the enviroment agency by the end of the week. The problem about being a concerned individual is that the refrigerant is pretty well hidden. I will have to give the enviromental people a good description of were it is. Thinking about it as well they have at least 75 kilo's of reclaimed contaminated refrigerant they they don't seem to want to dispose of.
    Neil
  19. #19
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Re: hydrocarbons
    ........the refrigerant is pretty well hidden. I will have to give the enviromental people a good description of were it is.
    I expect they will be able to find it.
    They will start with a demand to see all the relevant records, etc. I believe that they have the right of entry if they suspect an offence.
    Be very careful with your facts.
    You will still need to work when the dust has settled and this is a small industry with a big grapevine.
    ________
    Chevrolet Monte Carlo specifications
  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51
    Re: hydrocarbons
    So we're not talking about vast quantities then. This is only just over a large cylinder. But, that said, it can't be vented.
  21. #21
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21
    Re: hydrocarbons
    You are right Argus.
    I'm not feeling so bitter now. The best thing for me to do would be to contact the M.D of the company and tell him that he is still storing the refrigerant. Because the level of communication in the company is not so good he probanly does even know that he has got it. If I email him and tell him he can kick sum ass and get it sorted without it getting dirty. Especially if he thinks he will have to pay out a few grand in fines.
    Neil
Similar Threads
  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Last Post: 23-03-2010, 12:39 PM
  2. Propylene
    By Apoc in forum Refrigerants
    Last Post: 02-04-2004, 09:33 PM
  3. R290 Care 50
    By ralph feria in forum Refrigerants
    Last Post: 24-02-2004, 02:53 AM
  4. Regulation regarding hydrocarbons in an cascade
    By DaBit in forum Fundamentals
    Last Post: 19-01-2004, 12:42 PM
  5. Hydrocarbons
    By subzero*psia in forum Refrigerants
    Last Post: 04-04-2001, 12:50 AM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts