    Question Suction temp



    Hello all.

    Does any one have any idea of what the highest suction line temps that manufacturers rate for sealed units before they start to give trouble with overheating? (In particular Hermitique.)

    Reason I ask this is because I know of a system serving a hotel that has an extra long pipe run and I noticed that the suction line is not very cool due to the length of it.Also the liquid line is strapped to the suction line also increasing the superheat.

    I did once check the suction line temp and I think it was about 23 degrees c. The compressor itself is always quite hot to touch also.My belief is that eventually the excessive superheat will eventually damage the compressor.I have raised my concerns about this to another fridgy but he thinks I am worrying needlesly.Apart from this the system works perfectly.

    I have thought about maybe setting up some kind of desuperheating set up on it.

    Thanks all.
    Last edited by Temprite; 27-05-2005 at 12:11 PM.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Suction temp

    Hi Temprite,

    You can add an injection valve between the liquid and the suction lines to cool the compressor if it gets too hot. Does it?

    Chemi

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Suction temp

    Quote Originally Posted by chemi-cool
    Hi Temprite,

    You can add an injection valve between the liquid and the suction lines to cool the compressor if it gets too hot. Does it?

    Chemi

    Chemi, you mean on scroll compressors dont you?? Not on hermetics,
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Suction temp

    Hi Temprite,

    I would insulate the suction pipe and also make sure you are not going to over condense with a very long liquid line.
    If by the time liquid line reaches tev it is quite cold you could open the tev up a touch or move the senser bulb further down the suction to increase work load and cool comp down. ...(just a thought, too tired to think about it properly so don`t nobody shout at me)

    You could either stick a comp cooling fan on or make the cond fan spin the other way to draw fresh air over comp then through cond if comp is getting very hot.
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Suction temp

    Quote Originally Posted by chillin out
    Hi Temprite,

    I would insulate the suction pipe and also make sure you are not going to over condense with a very long liquid line.
    If by the time liquid line reaches tev it is quite cold you could open the tev up a touch or move the senser bulb further down the suction to increase work load and cool comp down. ..
    Thanks for the comments all.

    Chillin
    System runs temprite systems, no TX valves low side float.
    I have thought about insulating suction line and pulling liquid line away from it that would certainly help.

    I spoke to the wholesale company that deals in hermitique and they said that the suction temp was to high, but they couldn't give me a value of which it should be kept under.

    Aiyub
    Why no desuperheating on hermetics?

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Suction temp

    What is a Temprite system?
    What brand of compressors?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: Suction temp

    Peter_1 a temprite is a beer dispensing unit. You could almost call it a shell & tube evaporator..where the liquid refrigerant in in the shell ans the beer is in the coils. The liquid level is controlled by a low side float and the evap pressure maintained by a 750 valve.

    Temprite..On a long suction run you may be getting oil return problems and also excessive pressure drop High superheats will also cause high discharge temperatures and combine these factors and your compression ratio will increase. this will reduce the life of the compressor. High superheats also mean a decrease in the density of the refrigerant meaning that there is less refrigerant pumped per stroke of the compressor. This increases running time and electrical consumption. I have done a lot of temprite work and you can email me if you wish. I notice you are also in Australia..I am in Tasmania
    100% is possible 100% of the time

  8. #8
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Suction temp

    Peter

    Compressor is a Hermitique(4 or 5 hp I think.)and Deejay has already explained a temprite.

    Deejay
    Compressor origonally was a belt driven type as most of these old pub systems were.compressor cooling wasnt a big factor.The old belt compressor has been changed and a hermetic put in its place it has a remote condenser.System runs really well just has a very high suction temp.(Any suggestions?)

    Just to get off the topic.
    Is it true that in Launceston somewhere on a pub there is a system running with a PVC suction line? (Being from Tassie I thought you might know of this.

    Regards.

  9. #9
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: Suction temp

    I dont know about using PVC for suction line but I have students from launceston tomorrow so will ask them....but I doubt it....the pvc would deteriorate to quick
    Anyway...what size was the compressor that came off & what size is the hermetic..it sounds to me as if the hermetic isnt big enough for the capacity required...therefore high suction pressures...also is there an oil trap on the compressor discharge and also a surge tank on the suction line?? also what beer temperatures are you getting and what setting is the 750 valve...
    100% is possible 100% of the time

  10. #10
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: Suction temp

    I would suggest measuring the pressure at the 750 valve....and then the pressure at the compressor and see how much pressure drop your getting....is the suction line exposed to sun or any other heat source that could increase the superheat.....how much superheat are you getting...I think you said the temp was 23C at the compressor....which means you would be getting around 21K superheat which is way way to much.....
    100% is possible 100% of the time

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Suction temp

    Quote Originally Posted by Deejey
    ..;Peter_1 a temprite is a beer dispensing unit....
    Where can i find some info of this?
    Chemi, you remember I once send you a description long time ago (a scan of a Refr. book) of an ancient beer cooler system? Well, it seems not that ancient at all and it's still used in AUS.
    Here in Belgium - the land of the beers - we always use an ice bank with a double coil in it: a coil for the beer and a coil for the refrigerant.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Suction temp

    Quote Originally Posted by Peter_1
    Where can i find some info of this?
    Chemi, you remember I once send you a description long time ago (a scan of a Refr. book) of an ancient beer cooler system? Well, it seems not that ancient at all and it's still used in AUS.
    Here in Belgium - the land of the beers - we always use an ice bank with a double coil in it: a coil for the beer and a coil for the refrigerant.
    Peter read that post about the ancient beer cooler.

    That is indeed a temprite system and yes they are ancient its just that the pubs havent got off their backsides to change them yet.

    Still a fair amount of pubs using them.When they get around to replacing them they usually go to a glycol system.When you have several temprites on one system they have pretty large gas charge.

    We use ice banks here too,but I think glycol is becoming the popular choice.

    One thing I have noticed is that some temprites just dont operate properly on anything other than r12 unless they are designed for r22 then their usually ok.

    When I chose my user name I thought temprite was a fairly australian refrigeration term, as did 750 valve I would say.

  13. #13
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Suction temp

    Deejay.

    System has an oil seperator and a surge tank.

    I havent checked the setting on the 750 valve but it is probably around 0 deg c.

    They never complain about the beer in there.(unless there is a power failure.) I think last time I checked it was about 2 deg c.

    The suction line and liquid line are strapped together, if I seperated these and insulated suction line this would make a difference.if it was still a belt driven unit it wouldnt be a problem.

    Ever had a temprite that wont operate properly on anything other than r12? Try them on any other gas than r 12 and they have no recovery.Usually the drop ins are ok but not always.

  14. #14
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: Suction temp

    Temprite...I would indeed seperate the lines and insulate the suction....it should have a surge tank fitted to prevent short cycling whenever a beer is pulled..it would help to insulate that too.
    100% is possible 100% of the time

  15. #15
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Suction temp

    Quote Originally Posted by Temprite
    Deejay.

    System has an oil seperator and a surge tank.
    Deejay system definitely has a surge tank fitted but not insulated.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Suction temp

    Quote Originally Posted by Temprite
    .....as did 750 valve I would say.
    Ohhhhh...i thought it was that thing under his nose in his Avatar LOL
    BTW, next dump question , what is a 750 valve?

    Regarding the Temprite system again. These system are much smaller then the systems we use here with glycol. You always need a big space to install the ice bank and the Temprite system seems much more compact.
    You don't need an agitating mixer, no glycol, ...
    How do they manage the oil return in these systems? I once read it was done with some sort of a cotton cloth which was floating on the vaporising liquid.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: Suction temp

    Peter_1
    Temprite systems have an oil seperator which includes a high side float fitted to the discharge. when oil gets into a temprite it does not return and affects the beer temperature.
    A 750 valve works the same as a evaporator pressure regulator. You maintain the saturation temperature in the temprite by adjusting the pressure with the 750 valve the same as you maintain the sat temp in an FDC by adjusting the EPR.
    100% is possible 100% of the time

  18. #18
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Suction temp

    Peter
    What more could I say.....

    Sometimes temprite will get oil binding,due to oil taking up space of liquid refrigerant.Doesnt happen much if oil seperator is working.

    You can fix this by shutting hand valves and removing temprite and charge into suction line.By turning upside down when you do this the oil goes back into the sump.

    I am trying to get hold of an old manual on temprites (might take some time).If i can I will post on this thread.

  19. #19
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: Suction temp

    I think I have an old kelvinator temprite manual somewhere...will look tomorrow...havent seen it for ages..but have got it somewhere....
    100% is possible 100% of the time

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  3. Condensing temp in refrigeration
    By anup in forum Fundamentals
    Replies: 1
    Last Post: 02-10-2005, 11:18 AM
  4. Multiplex For Low Temp and Medium Temp
    By allanbaker in forum Technical Discussions
    Replies: 0
    Last Post: 28-11-2002, 10:15 AM
  5. Engineering problem? Hmmmmm
    By bernie in forum Trouble Shooting
    Replies: 71
    Last Post: 26-06-2002, 03:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •