    Daikin UF fault code



    Help. I have a Daikin 3 phase twin-split system bringing up a UF fault code instantly when switched on. It's been running for 10 years, have checked interconnecting, remote, external pump, Daikin tell me one of the PCB's is down either on one of the indoor units (cassettes) or on the outdoor. Daikin can't tell me which one and say there's no way to test them, it's pot luck. Please help.



  2. #2
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin UF fault code

    Whats the model number?
    No longer Active

  3. #3
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin UF fault code

    i have had this before and it was induced voltage on the interconnecting cables between the indoor and outdoor, measure this voltage and you will probably find it is higher than 50v dc

  4. #4
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin UF fault code

    Best way to determine.

    System is just 2 indoor units connected to an outdoor unit. eg ( 4hp X 2 indoor ) - (8hp outdoor)

    If you want to find faulty PCB.

    Disconnect communication on one unit at a time. This will give you electrically a 4hp indoor connected to a 8hp outdoor. If the system still has fault try doing same to other fan coil. If problem fixed then previous indoor PCB faulty. If still have problem then check outdoor PCB or outdoor to indoor wiring.
    No longer Active

  5. #5
    Join Date
    Jun 2006
    Location
    Wales
    Posts
    9
    Rep Power
    0

    Re: Daikin UF fault code

    Thank you my friend, get a job with Daikin, you've been more help in one answer than I've ever got from Daikin, all I got was one word answers. Will let you know how I get on.

  6. #6
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Daikin UF fault code

    Hi according to the below chart it seems you got your wires crossed




    DAIKIN MALFUNCTION CODES
    Code Place Description
    AO Indoor Error of external protection device
    A1 Indoor PCB defect
    A3 Indoor Malfunction of drain Level control system
    A5 Indoor Freeze-up prevention
    A6 Indoor Fan motor lock, Overload
    A7 Indoor Malfunction of swing motor flap
    A9 Indoor Malfunction of EEV
    AF Indoor Drain level above limit (clogging)
    AJ Indoor Malfunction of capacity set device
    C3 Indoor Malfunction of drain thermistor
    C4 Indoor Malfunction of liquid pipe thermistor
    C5 Indoor Malfunction of gas pipe thermistor
    C7 Indoor Lower louvre limit switch/motor
    C9 Indoor Malfunction of air thermistor
    CC Indoor Malfunction of moisture sensor
    CA Indoor Malfunction of discharge air thermistor
    CJ Indoor Malfunction of remote control thermistor
    CE Indoor Malfunction of radiant heat sensor
    E0 Outdoor Activation of outdoor safety device
    E1 Outdoor PCB defect
    E3 Outdoor Activation of high pressure switch
    E4 Outdoor Activation of low pressure switch
    E5 Outdoor Activation of compressor over heat protection
    E5 Outdoor Compressor motor lock
    E6 Outdoor Compressor start up error
    E6 Outdoor Standard compressor lock/overcurrent
    E7 Outdoor Fan motor lock, Overload
    E8 Outdoor Inverter input overcurrent
    E9 Outdoor Malfunction of EEV
    EA Outdoor Four way valve defective.
    F3 Outdoor Abnormal discharge pipe temperature
    F6 Outdoor Refrigerant overcharged
    FC Outdoor Low pressure drop.
    H3 Outdoor High pressure switch defect
    H4 Outdoor Low pressure switch defect
    H6 Outdoor Compressor motor position detection sensor error
    H7 Outdoor Fan motor position detection sensor error
    H8 Outdoor Current transformer error
    H9 Outdoor Malfunction of air thermistor
    J1 Outdoor Malfunction of pressure sensor
    J2 Outdoor Current sensor malfunction
    J3 Outdoor Malfunction of discharge pipe thermistor
    J4 Outdoor Low pressure saturation thermistor
    J5 Outdoor Malfunction of suction pipe thermistor
    J6 Outdoor Malfunction of heat exchanger thermistor
    J7 Outdoor Malfunction of heat exchanger liquid thermistor
    J8 Outdoor Malfunction of liquid pipe thermistor
    J9 Outdoor Malfunction of gas pipe thermistor
    JA Outdoor Malfunction of discharge pipe pressure sensor
    JC Outdoor Malfunction of suction pipe pressure sensor
    JH Outdoor Malfunction of oil temperature sensor
    L0 Outdoor Malfunction of inverter
    L3 Outdoor Electronic component box overheat
    L4 Outdoor Inverter cooling defect
    L5 Outdoor Comp motor ground fault, Short circuit
    L6 Outdoor Compressor motor grounding/short circuit
    L7 Outdoor Total input overcurrent
    L8 Outdoor Comp overload, Motor disconnected
    L9 Outdoor Compressor lock
    LA Outdoor Power unit malfunction
    LC Outdoor Transmission between inverter & outdoor
    P1 Outdoor Inverter over ripple
    P3 Outdoor Thermistor abnormality
    P4 Outdoor Power unit humidity sensor malfunction
    PJ Outdoor Failure of capacity set resistor
    U0 System Shortage of refrigerant or EEV failure
    U1 System Negative phase, Open phase
    U2 System Power supply insufficient
    U3 System Wiring check operation not executed
    U3 System Mismatch of indoor and outdoor units (Split only)
    U4 System Transmission between indoor units
    U5 System Transmission to remote controller
    U6 System Malfunction transmission outdoor to BP unit
    U7 System Transmission between outdoor units
    U7 Outdoor Malfunction between outdoor boards(RMX/RX RK)
    U8 System Transmission between master & slave R/C
    U9 System Transmission error between indoor to outdoor
    UA System Excessive number of fancoils
    UC System Address duplication of central controllers
    UE System Transmission error between indoor & central
    UF System Refrigeration system not set/wiring - piping
    UF System Terminals 1 and 3 crossed (Split/Skyair)
    UH System System error, Refrigeration system set up
    M1 System PCB defect
    M8 System Transmission error between central controllers
    MA System Improper combination of optional controllers
    MC System Address duplication, Improper setting
    64 VAM Indoor unit air thermistor error
    65 VAM Outside air thermistor error
    68 VAM
    6A VAM Damper system alarm
    6A VAM Damper system and thermistor error
    6F VAM Malfunction of remote controller
    6H VAM Malfunction of door switch or connector
    94 VAM Internal transmission error
    Grey fault codes, system still runs, but check ASAP

  7. #7
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin UF fault code

    meab

    That is correct on some systems however this system is a little different. We have 2 fancoils that operate as one. They share the one outdoor unit and cycle on/off at the same time. They can't cycle independently. The controller wires to the first unit and controls the second unit through the no 2 wire on the interconnect that daisy chains between the 2 units. Wire go from out to 123 on first indoor and then to 123 on second indoor. Cant wire both fancoils direct from outdoor. Won't work. Unit will automatically set up twin setting on power up.
    No longer Active

  8. #8
    Join Date
    Nov 2009
    Location
    Leeds England
    Age
    41
    Posts
    5
    Rep Power
    0

    Re: Daikin UF fault code

    Hi Deyna

    Check there is nothing wired in to terminals 1&2 ie condensate pump. I have seen this cause this type of problem as Terminal 2 is neutral on the newer daikin units and control/data on older units. If somone has changed a pump recentley they may have wired it incorrectly.

Similar Threads

  1. Daikin UH fault code
    By frostice55 in forum Trouble Shooting
    Replies: 1
    Last Post: 25-01-2010, 09:11 AM
  2. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Replies: 11
    Last Post: 28-07-2009, 01:26 AM
  3. Daikin fault code E6
    By casino in forum Air Conditioning
    Replies: 4
    Last Post: 24-11-2007, 12:35 PM
  4. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  5. Daikin FUYP71BV1 fault code
    By Andy W in forum Air Conditioning
    Replies: 6
    Last Post: 15-02-2007, 09:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •