31-07-2010, 08:44 AM #1
R422d advice for a -21 freezer
Hi all, we have just retrofited two -21 freezers with r422d and are having problems with getting them below -16. suction pressures just below 1 bar and discharge pressure 13 to15 bar, ambeient inplant room 27 to 31 degrees c air on to condenser 17 to21c air off 27c. liquid line temp just after reciver 30 to 35 c . any help would be great thanks.
-
31-07-2010, 09:15 AM #2
Re: R422d advice for a -21 freezer
What was the original refrigerant?
-
31-07-2010, 11:10 AM #3
Re: R422d advice for a -21 freezer
Is this an R22 retrofit?
What suction superheat is it running?
'just under a bar' is about -24c, i'm wondering if the txv is overfeeding the evaporator.
I think there is also a drop in capacity with a lot of the replacement refrigerants.
-
31-07-2010, 07:41 PM #4
Re: R422d advice for a -21 freezer
THANKS FOR YOUR REPLYS. The system was on r22. evaps are in the gods and the tev's are in the end panals so unable to get the superheat measurments easily. they did run ok for a few weeks but have just recently started playing up.
-
01-08-2010, 09:21 PM #5
Re: R422d advice for a -21 freezer
any body out there.
-
01-08-2010, 10:20 PM #6
Re: R422d advice for a -21 freezer
I'm sure you will have checked this but there is often problems with 'o' rings failing after R22 is replaced, so shortage of refrigerant would be a thing i'd check for.
What make compressors are in the system? I have seen waxing problems of txvs after conversion, particularily with maneurops.
The other things to check are anything not refrigerant related, as its easy to get tunnel vision when something has been changed recently, compressors pumping ok, driers ok, defrost working ok, no air leaks into the rooms, temperature display acurate, etc.
Jon
-
02-08-2010, 07:07 AM #7
Re: R422d advice for a -21 freezer
Why are you guys playing with darn retrofits?
Don't touch R22. Don't fix it if it ain't broken.
-
02-08-2010, 11:22 AM #8
Re: R422d advice for a -21 freezer
Have a look here, note a 20% capacity drop with R422D, maybe there isn't enough time in the day for it to keep up?
http://www.tecumsehcoolproducts.com/...-RD-0003-E.pdf
Pleanty of other useful info too!
Jon
-
02-08-2010, 12:05 PM #9
Re: R422d advice for a -21 freezer
Well said NONICKNAME!! Leave the bloody R22 alone.!
-
06-08-2010, 04:09 PM #10
Re: R422d advice for a -21 freezer
Thanks chaps for advice, turns out both systems short of gas. oh joy. thanks again you lot.
Similar Threads
-
Maytag Freezer TOO Cold (and fridge also)
By ptb626 in forum DomesticReplies: 1Last Post: 17-08-2010, 01:56 PM -
Chiller/ Freezer Partly Frosting
By Mistral1962 in forum Trouble ShootingReplies: 4Last Post: 02-05-2010, 06:44 AM -
Fisher & Paykell freezer problem
By jack in oz in forum DomesticReplies: 4Last Post: 01-05-2010, 02:27 AM -
Blast Freezer Within Freezer
By rickmor in forum Technical DiscussionsReplies: 4Last Post: 18-06-2009, 03:37 AM -
Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
By sumnerpa in forum Trouble ShootingReplies: 1Last Post: 19-08-2008, 03:16 PM