06-08-2010, 12:47 PM #1
Re: Daikin UF fault code
Hi Deyna
Check there is nothing wired in to terminals 1&2 ie condensate pump. I have seen this cause this type of problem as Terminal 2 is neutral on the newer daikin units and control/data on older units. If somone has changed a pump recentley they may have wired it incorrectly.