Thread: control group setpoints
-
30-07-2010, 12:47 PM #1
control group setpoints
Hey Guys,
Sabroe 125 hp screw setpoints: control is set at 4"hg with cut-in setpoint of 0.0 psig ...is this correct ?
-
30-07-2010, 08:04 PM #2
Re: control group setpoints
for what refrigerant, appliance and application?
-
01-08-2010, 05:41 PM #3
-
01-08-2010, 07:04 PM #4
-
02-08-2010, 12:04 AM #5
Re: control group setpoints
Yea sorry we do use ammonia.im new at this job but im pretty sure that we need to run a vacuum..Why would you not need a vacuum .Without suction will cause problems to wouldnt it ???We dont have a air curtain and 1 evap is directly above the door going into the cold storage.when the door opens up and lot of cold air rushes out causes fog in the loading bay ands water on floors.Im thinking we are wasting energy.
-
02-08-2010, 07:04 AM #6
-
02-08-2010, 02:01 PM #7
Re: control group setpoints
yes 4 inches of mercury.what would be the proper setting in your mind?
-
02-08-2010, 03:43 PM #8
Re: control group setpoints
4inHG are 0.14 barg and correspond to -30°C evaporating temperature. Is this a low stage of a cascade system? What is the condensing temperature?
-
02-08-2010, 04:33 PM #9
-
02-08-2010, 06:52 PM #10
Re: control group setpoints
That doesn't answer my question.
What is the condensing temperature or pressure?
-
02-08-2010, 07:04 PM #11
-
02-08-2010, 07:30 PM #12
Re: control group setpoints
I don't think you can do it that way. 8 barg high side, 0.15 barg low side would cause a discharge temperature of 160-170°C.
I think you need to go back to the drawing board.
-
03-08-2010, 01:51 AM #13
Re: control group setpoints
yea sorry my bad discharge temp is 88 degrees C,discharge pressure is 120 psi,,operating pressure is 70 psi,compressor slide valve is 100% 1.3 inches of mercury,, ST is -29.0 degrees C.This compressor is not working properly.
The compressor that we have that is the same model and is working correctly has a discharge temp of 69 C ,discharge pressure 120 psi,operating pressure of 120 psi,3-4 inches mercury ST is -29.0 C.
Im new to this profession and appreciate all help and advice.
-
03-08-2010, 07:00 AM #14
Re: control group setpoints
The first compressor is starving, as I see it. Maybe, somebody with more insight on ammonia can help you more.
Similar Threads
-
Lost Remote Control for Split System AC
By kiamaian in forum Air ConditioningReplies: 5Last Post: 12-04-2009, 06:12 PM -
Airwell Florida Inverter Air Condition - in need of help
By AndY1 in forum Air ConditioningReplies: 21Last Post: 05-07-2008, 10:48 AM -
Control group best painting practices.
By zolimer in forum NH3Replies: 4Last Post: 05-04-2008, 02:22 PM -
Control scenario
By Mike Hopkins in forum Technical DiscussionsReplies: 5Last Post: 14-09-2007, 11:25 AM -
New Capacity Control Solution
By embrown in forum New TechnologiesReplies: 19Last Post: 30-12-2003, 01:33 PM