    control group setpoints



    Hey Guys,

    Sabroe 125 hp screw setpoints: control is set at 4"hg with cut-in setpoint of 0.0 psig ...is this correct ?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: control group setpoints

    for what refrigerant, appliance and application?

  3. #3
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: control group setpoints

    Quote Originally Posted by NoNickName View Post
    for what refrigerant, appliance and application?
    Hey,

    R17,Cold Storage for frozen fish/shrimp,3 evaps

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: control group setpoints

    Quote Originally Posted by stanthonycold View Post
    Hey,

    R17,Cold Storage for frozen fish/shrimp,3 evaps

    Surely you mean R717 (Ammonia )
    In which case you are running way to low.
    Running in a vacuum can cause all sort of issues.
    Grizzly

  5. #5
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: control group setpoints

    Quote Originally Posted by Grizzly View Post
    Surely you mean R717 (Ammonia )
    In which case you are running way to low.
    Running in a vacuum can cause all sort of issues.
    Grizzly
    Yea sorry we do use ammonia.im new at this job but im pretty sure that we need to run a vacuum..Why would you not need a vacuum .Without suction will cause problems to wouldnt it ???We dont have a air curtain and 1 evap is directly above the door going into the cold storage.when the door opens up and lot of cold air rushes out causes fog in the loading bay ands water on floors.Im thinking we are wasting energy.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: control group setpoints

    Quote Originally Posted by stanthonycold View Post
    Hey Guys,

    Sabroe 125 hp screw setpoints: control is set at 4"hg with cut-in setpoint of 0.0 psig ...is this correct ?
    No, it's not. What do you mean by 4"hg? 4 inches of mercury?

  7. #7
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: control group setpoints

    yes 4 inches of mercury.what would be the proper setting in your mind?

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: control group setpoints

    4inHG are 0.14 barg and correspond to -30°C evaporating temperature. Is this a low stage of a cascade system? What is the condensing temperature?

  9. #9
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: control group setpoints

    Quote Originally Posted by NoNickName View Post
    4inHG are 0.14 barg and correspond to -30°C evaporating temperature. Is this a low stage of a cascade system? What is the condensing temperature?
    suction is -34f/4.7"hg, 3 rotary screw ,6 flooded evaps

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: control group setpoints

    That doesn't answer my question.
    What is the condensing temperature or pressure?

  11. #11
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: control group setpoints

    Quote Originally Posted by NoNickName View Post
    That doesn't answer my question.
    What is the condensing temperature or pressure?

    130 psi .........

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: control group setpoints

    I don't think you can do it that way. 8 barg high side, 0.15 barg low side would cause a discharge temperature of 160-170°C.
    I think you need to go back to the drawing board.

  13. #13
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: control group setpoints

    Quote Originally Posted by NoNickName View Post
    I don't think you can do it that way. 8 barg high side, 0.15 barg low side would cause a discharge temperature of 160-170°C.
    I think you need to go back to the drawing board.
    yea sorry my bad discharge temp is 88 degrees C,discharge pressure is 120 psi,,operating pressure is 70 psi,compressor slide valve is 100% 1.3 inches of mercury,, ST is -29.0 degrees C.This compressor is not working properly.

    The compressor that we have that is the same model and is working correctly has a discharge temp of 69 C ,discharge pressure 120 psi,operating pressure of 120 psi,3-4 inches mercury ST is -29.0 C.

    Im new to this profession and appreciate all help and advice.

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: control group setpoints

    The first compressor is starving, as I see it. Maybe, somebody with more insight on ammonia can help you more.

Similar Threads

  1. Lost Remote Control for Split System AC
    By kiamaian in forum Air Conditioning
    Replies: 5
    Last Post: 12-04-2009, 06:12 PM
  2. Replies: 21
    Last Post: 05-07-2008, 10:48 AM
  3. Control group best painting practices.
    By zolimer in forum NH3
    Replies: 4
    Last Post: 05-04-2008, 02:22 PM
  4. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •