    Freezer Room Design



    Dear All,

    Is there any design standard where to install the evaporators units in the cool rooms ?.

    what we have here the the evaporators was install on the top of the door, so every times when the door open the evaporator will suck the outside air into the room & moisture will condense at the evaporator fin coil & form the Ice-wall & reduce the freezer performance.

    Even the system is having the defrost cycle, we still having severe blockage over period of time since our enviroment huminity is 80%.

    From my observation most of the freezer room design was having the evaporators at the end of the cool room or at the side away from the door. In this condition I'm notice, whe we open the door the positive pressure will blow-out toward the doors.

    beside the best practice, I need to look for some standard or article by the expert to convince my management the by relocate the evaporator units away from the doors will reduce the amount of moisture being suck-in.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Freezer Room Design

    Whenever possible, refrigerating air-cooling units should be
    located away from enclosure entrance doors and passageways. This
    practice helps reduce coil frost accumulation and fan blade icing.
    The cooler manufacturer’s installation, start-up, and operation instructions
    generally give the best information.
    Refrigeration, CHAPTER 42
    FORCED-CIRCULATION AIR COOLERS
    2006 ASHRAE Handbook

  3. #3
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: Freezer Room Design

    On some of the small walk-in freezers and fridges I use to install, we would put in evaporator fan-stop switches on the doors. So the evaporator fan stops sucking in too much ambient air. Of course the compressor still runs, so we always ensured the customer was aware not to leave the door ajar for too long. Quite handy on small units where you haven't got a lot of location choice.
    If at first you DO succeed, try to hide your astonishment!!

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Freezer Room Design

    Quote Originally Posted by acnerd View Post
    On some of the small walk-in freezers and fridges I use to install, we would put in evaporator fan-stop switches on the doors. So the evaporator fan stops sucking in too much ambient air. Of course the compressor still runs, so we always ensured the customer was aware not to leave the door ajar for too long. Quite handy on small units where you haven't got a lot of location choice.
    In the old days, we used to interlock the fan with the interior light, so that when the light was on the fan was off.
    We had one major complaint from a Mr Noah on the ARK he his staff kept leaving the light on and the fan off.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Freezer Room Design

    Nearly all unit coolers are ceiling-mounted
    and should be placed (1) so they do not discharge air at any doors or
    openings, (2) away from doors that do not incorporate an entrance
    vestibule or pass to another refrigerated enclosure to keep from
    inducing additional infiltration into the enclosure, and (3) away from
    the airstream of another unit to avoid defrosting difficulties.
    ..............................

  6. #6
    Join Date
    Aug 2010
    Location
    USA
    Age
    54
    Posts
    10
    Rep Power
    0

    Re: Freezer Room Design

    Standards for evaporator placement? I never seen one, very typical of the refrigeration trade.

    Besides ASHRAE try NSF #7 if the freezer has edible products, and try Heatcraft refrigeration manual.

  7. #7
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Freezer Room Design

    Door or air curtains should be fitted as a std in that enviroment

  8. #8
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Freezer Room Design

    Follow this link and open the "Heatcraft IOM" link. Page 3 has your answer.

    http://www.hvacrinfo.com/loadcalcs.htm
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  9. #9
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Freezer Room Design

    Dear Sir,

    Please view the attachement
    Best regards
    Attached Images Attached Images
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  10. #10
    Join Date
    Jun 2007
    Location
    Sri Lanka
    Posts
    88
    Rep Power
    0

    Re: Freezer Room Design

    It is quite strange that the evap position. Best solution is to relocate the evap. Install an electric or PVC air curtain. If you are constraint with space in the cooler, you can interlock with the door and evap fans. But you have to be very careful here. The compressor will flood with liquid. Do not take this risk. Cut off the solenoid valve and evap fans when the door is opened. Then the system will get pump down and stops. fficeffice" />>>

Similar Threads

  1. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Replies: 35
    Last Post: 09-08-2010, 12:10 PM
  2. freezer room equipment
    By jack smith in forum Tools and Calculators
    Replies: 4
    Last Post: 12-06-2010, 05:27 AM
  3. Freezer Room flooring design and CAD works
    By riazahmadmalik in forum Technical Discussions
    Replies: 12
    Last Post: 07-01-2010, 08:08 AM
  4. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •