    Air in the system



    Hi Guys,

    I hope you can clarify me about the following:
    Several times I heard to say that if a needle of the gauge is instable it could mean air or the system...Why is that? If it's that true I think not every time that happens it means that is air, right?


    To make progress is never good enough, I want to do better and better and better

  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Air in the system

    PLease don't forget of me...
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Air in the system

    No not the only reason for your guage fluttering. U sure your guage is not faulty?

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Air in the system

    I haven't any gauge with problems. Just want understand what's the reason why the air influence the fluttering...what have so especial comparing with the refrigerant fluids in vapour state?
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Air in the system

    Quote Originally Posted by Sandro Baptista View Post
    Hi Guys,

    I hope you can clarify me about the following:
    Several times I heard to say that if a needle of the gauge is instable it could mean air or the system...
    I would say rubbish!

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Air in the system

    Air in the system? If its the high pressure gauge i'd say the discharge service port is open too much but air contamination will cause that needle to wind over somewhat!

  7. #7
    Join Date
    Jul 2010
    Location
    England
    Age
    64
    Posts
    8
    Rep Power
    0

    Re: Air in the system

    Hi do you mean the discharge or suction guage?

    1: Is it slowly moving up and down.?
    2: Or is it moving fast?

    Look forward to seeing your reply

    Steve

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Air in the system

    No, it's plain rubbish. That is only true in a water system, when bubbles flow. In a refrigeration circuit, air just stands in the highest point, that is the generally the condenser manifold of top half of the coil.

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Air in the system

    Air in a system will cause the high pressure to rise very high.
    If you have air in the system you will have to change the refrigerant, drier and compressor oil.

    When the niddle in the discharge gauge is instable > very instable, it tells you something of the condition of the valves and piston rings.

    Rubbish in the system is totally a different story.....
    Last edited by chemi-cool; 30-07-2010 at 04:05 PM.

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Air in the system

    Hope he doesn't have rubbish in the system.

  11. #11
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Air in the system

    Quote Originally Posted by mikeref View Post
    Air in the system? If its the high pressure gauge i'd say the discharge service port is open too much but air contamination will cause that needle to wind over somewhat!
    Why? Please give me a physics explanation.

    Quote Originally Posted by Old cooler View Post
    Hi do you mean the discharge or suction guage?

    1: Is it slowly moving up and down.?
    2: Or is it moving fast?

    Look forward to seeing your reply

    Steve
    No problem with any gauges. It's just sometimes I heard talk about the instability of the gauges associated to the presence of the air.



    Quote Originally Posted by NoNickName View Post
    No, it's plain rubbish. That is only true in a water system, when bubbles flow. In a refrigeration circuit, air just stands in the highest point, that is the generally the condenser manifold of top half of the coil.
    Yes, I also agree.
    To make progress is never good enough, I want to do better and better and better

  12. #12
    Join Date
    Aug 2010
    Location
    Brisbane
    Age
    39
    Posts
    7
    Rep Power
    0

    Re: Air in the system

    This would be the discharge port is open to much which causes the gauge to flutter, if air is in the system it will sit in your condenser i dont belive air would cause your gauge to flutter, your head pressure would be very hight but if you had air in the system.

    if a water system has air in it the gauges will move all over the place but it will sit in the highest point which there should be auto bleads at this point.

  13. #13
    Join Date
    Aug 2010
    Location
    USA
    Age
    54
    Posts
    10
    Rep Power
    0

    Re: Air in the system

    My first post...

    If your gauges are fluttering I would suspect that you need to get new ones or at least ones that have liquid damping. Otherwise you have a reciprocating compressor which has either no attenuator or an improper sized one. Try measuring the pressure as far away from the compressor.

    The fluttering is proportional to the number of pistons, rpm, compression ratio

  14. #14
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Air in the system

    Quote Originally Posted by shieldcracker View Post
    My first post...

    If your gauges are fluttering I would suspect that you need to get new ones or at least ones that have liquid damping. Otherwise you have a reciprocating compressor which has either no attenuator or an improper sized one. Try measuring the pressure as far away from the compressor.

    The fluttering is proportional to the number of pistons, rpm, compression ratio
    "...have liquid damping."

    Yes typical they are fill with glycerin. However at this moment no problem I have with gauges. Read my first post. thanks.



    "Otherwise you have a reciprocating compressor which has either no attenuator or an improper sized one."

    An oil separator will help a lot.


    "The fluttering is proportional to the number of pistons, rpm, compression ratio"

    Not necessary proportional to the number of pistons. Depending of the conception of the crankshaft more pistons could give less pulsations.


    Thanks Shieldcracker
    To make progress is never good enough, I want to do better and better and better

  15. #15
    Join Date
    Aug 2010
    Location
    australia
    Posts
    15
    Rep Power
    0

    Re: Air in the system

    As chemicool said the guage needle moving up and down rapidly on the high side would indicate that the compressor valves or piston compression is faulty. air will not move around with the refrigerant it will just sit in the highest point of the system.

  16. #16
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Air in the system

    Quote Originally Posted by razor007 View Post
    As chemicool said the guage needle moving up and down rapidly on the high side would indicate that the compressor valves or piston compression is faulty. air will not move around with the refrigerant it will just sit in the highest point of the system.
    I'm plenty agree.
    To make progress is never good enough, I want to do better and better and better

  17. #17
    Join Date
    Jul 2010
    Location
    England
    Age
    64
    Posts
    8
    Rep Power
    0

    Re: Air in the system

    I guess you must mean the discharge/high side then?
    Rapid pulsating is certainly the influence of a recip compressor

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. Residential R-22 system. HO added 134a
    By Magnapro in forum Technical Discussions
    Replies: 5
    Last Post: 26-05-2010, 09:12 PM
  3. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 04:18 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 04:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •