    Question carrier Supra 850 MT Please help



    I am trying to get an electrical diagram for the unit on one of our trucks.
    The electric motor is free but will not run and keeps tripping the breaker.
    Any help appreciated.

    Thanks.

    mike



  2. #2
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: carrier Supra 850 MT Please help

    Why do you need an electrical diagram for that?

    Just meter the motor out to check it is OK?

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: carrier Supra 850 MT Please help

    Quote Originally Posted by muller1 View Post
    I am trying to get an electrical diagram for the unit on one of our trucks.
    The electric motor is free but will not run and keeps tripping the breaker.
    Any help appreciated.

    Thanks.

    mike
    have you or an electrician checked the resistance of the motor,is the breaker strong enough ie the correct amperage,has the unit ran on this supply in the past.

  4. #4
    stormycgc's Avatar
    stormycgc Guest

    Re: carrier Supra 850 MT Please help

    have u checked the over load setting in the control box ? also is it tripping out due to the engine clutch trying to crank at same time due to a seized on clutch ?

  5. #5
    Join Date
    Feb 2009
    Location
    UK
    Posts
    14
    Rep Power
    0

    Re: carrier Supra 850 MT Please help

    Have you got 3 phases to motor? If not is the contactor and overload OK? I have had a few problems with Carrier contactors. Have you megger tested motor? If it all checks out Ok from memory I think there is a motor klixon in the circuit I have had problems with before.

  6. #6
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: carrier Supra 850 MT Please help

    Quote Originally Posted by transcoolchris View Post
    Have you got 3 phases to motor? If not is the contactor and overload OK? I have had a few problems with Carrier contactors. Have you megger tested motor? If it all checks out Ok from memory I think there is a motor klixon in the circuit I have had problems with before.
    No motor klixon in the circuit as far as I am aware?

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier Supra 444
    By ddocwra in forum Transport
    Replies: 14
    Last Post: 30-04-2010, 06:52 AM
  3. Carrier Supra 944 help please.
    By georgiajimbo in forum Transport
    Replies: 5
    Last Post: 06-10-2009, 02:21 PM
  4. Carrier Supra 650
    By Jwatdtr1878 in forum Trouble Shooting
    Replies: 0
    Last Post: 26-06-2009, 12:44 PM
  5. Carrier Supra
    By Vernon in forum Transport
    Replies: 6
    Last Post: 05-07-2008, 07:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •