    Dunno's Avatar
    Dunno Guest

    Anyone has Dorin condensing unit info



    I have a Dorin semi-hermetic condensing unit with 15 hp. I am confused with the
    1) min and max flowrate of the compressor
    2) what is the charging amount?


    Anyone used this model from Dorin before, can kindly reply this thread.. Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Anyone has Dorin condensing unit info

    Give us full model number of your condensing unit.
    http://www.dorin.com/jsp/Template1/SupportData.jsp

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Anyone has Dorin condensing unit info

    Positive displacement compressors, unless inverter driven, have a fixed flow rate. When inverter driven, the min and max frequency is specified on the compressor documentation, and is generally 25-70Hz for normal range, or 15-87Hz for the extended range.

    And condensing units do not have a charging amount, just because of their name: they are CONDENSING units, not a complete refrigerant circuit. The charge is undetermined.

  4. #4
    Dunno's Avatar
    Dunno Guest

    Re: Anyone has Dorin condensing unit info

    The model name is AUI2-HI1500CC

    It has a inverter, however the flowrate stated in the catalog is confusing..
    min flowrate is 19.53 m^3/h, too low for my application but it can provide the desired cooling capacity..

    I thought dorin condensing unit should have a max charging amount.. or should I say all condensing unit should have a max limit of charging refrigerant..

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Anyone has Dorin condensing unit info

    Quote Originally Posted by Dunno View Post
    The model name is AUI2-HI1500CC

    It has a inverter, however the flowrate stated in the catalog is confusing..
    min flowrate is 19.53 m^3/h, too low for my application but it can provide the desired cooling capacity..
    19.53÷73.23 m^3/h at 20÷75 Hz! I don't see what is confusing there!

    I thought dorin condensing unit should have a max charging amount.. or should I say all condensing unit should have a max limit of charging refrigerant..
    Generaly speaking, Max. charge should not exceed volume of receiver which is 15 l for that model.

    http://www.dorin.com/documents/Downl...4b_1LTZ027.pdf
    Last edited by nike123; 28-07-2010 at 12:18 PM.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Anyone has Dorin condensing unit info

    Quote Originally Posted by nike123 View Post
    19.53÷73.23 m^3/h at 20÷75 Hz! I don't see what is confusing there!
    My guess: this is not the air flow rate. It is the refrigerant volume flow rate. Is this what you find confusing? And for the max charge, it would be easier if you could give us an hint about the system.
    If you think the charge is too small, you could easily add an additional liquid receiver just after the existing one.
    Last edited by NoNickName; 28-07-2010 at 01:02 PM.

  7. #7
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: Anyone has Dorin condensing unit info

    19.53÷73.23 m^3/h at 20÷75 Hz is the displacement at 20 hz and 75 hz

Similar Threads

  1. water cooled condensing unit
    By sean1 in forum Commercial
    Replies: 5
    Last Post: 27-05-2010, 12:02 AM
  2. Sizing a condensing unit for a serve over counter
    By jimbo22 in forum Fundamentals
    Replies: 0
    Last Post: 25-11-2009, 04:50 PM
  3. Hanging a condensing unit
    By Abe in forum Air Conditioning
    Replies: 19
    Last Post: 01-10-2007, 09:16 PM
  4. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •