28-07-2010, 07:22 AM #1
Anyone has Dorin condensing unit info
I have a Dorin semi-hermetic condensing unit with 15 hp. I am confused with the
1) min and max flowrate of the compressor
2) what is the charging amount?
Anyone used this model from Dorin before, can kindly reply this thread.. Thanks
-
28-07-2010, 09:16 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Anyone has Dorin condensing unit info
Give us full model number of your condensing unit.
http://www.dorin.com/jsp/Template1/SupportData.jsp
-
28-07-2010, 10:00 AM #3
Re: Anyone has Dorin condensing unit info
Positive displacement compressors, unless inverter driven, have a fixed flow rate. When inverter driven, the min and max frequency is specified on the compressor documentation, and is generally 25-70Hz for normal range, or 15-87Hz for the extended range.
And condensing units do not have a charging amount, just because of their name: they are CONDENSING units, not a complete refrigerant circuit. The charge is undetermined.
-
28-07-2010, 11:08 AM #4
Re: Anyone has Dorin condensing unit info
The model name is AUI2-HI1500CC
It has a inverter, however the flowrate stated in the catalog is confusing..
min flowrate is 19.53 m^3/h, too low for my application but it can provide the desired cooling capacity..
I thought dorin condensing unit should have a max charging amount.. or should I say all condensing unit should have a max limit of charging refrigerant..
-
28-07-2010, 12:01 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Anyone has Dorin condensing unit info
19.53÷73.23 m^3/h at 20÷75 Hz! I don't see what is confusing there!
I thought dorin condensing unit should have a max charging amount.. or should I say all condensing unit should have a max limit of charging refrigerant..
http://www.dorin.com/documents/Downl...4b_1LTZ027.pdfLast edited by nike123; 28-07-2010 at 12:18 PM.
-
28-07-2010, 01:00 PM #6
Re: Anyone has Dorin condensing unit info
My guess: this is not the air flow rate. It is the refrigerant volume flow rate. Is this what you find confusing? And for the max charge, it would be easier if you could give us an hint about the system.
If you think the charge is too small, you could easily add an additional liquid receiver just after the existing one.Last edited by NoNickName; 28-07-2010 at 01:02 PM.
-
28-07-2010, 06:24 PM #7
Re: Anyone has Dorin condensing unit info
19.53÷73.23 m^3/h at 20÷75 Hz is the displacement at 20 hz and 75 hz
Similar Threads
-
water cooled condensing unit
By sean1 in forum CommercialReplies: 5Last Post: 27-05-2010, 12:02 AM -
Sizing a condensing unit for a serve over counter
By jimbo22 in forum FundamentalsReplies: 0Last Post: 25-11-2009, 04:50 PM -
Hanging a condensing unit
By Abe in forum Air ConditioningReplies: 19Last Post: 01-10-2007, 09:16 PM -
York/Bristol Condensing Unit
By Abe in forum CommercialReplies: 1Last Post: 03-02-2003, 07:46 PM -
Matching Evaporator with Condensing Unit
By Abe in forum Technical DiscussionsReplies: 12Last Post: 25-07-2001, 08:57 AM