    Oscillating Suction Line Temperature



    Hello,
    I have a 1500 BTU freezer in an Ice Cream Vending Machine that I am repairing. The unit was originally an R12 unit that I have converted to MP66. It was not working when I started the repair work and I have no idea what the correct R12 high side and low side pressures were. The unit label states that the charge should be 15 Oz of R12. I have taken 80% of this value (MP66 adjustment) leaving a 12 Oz MP66 charge. I have added a larger liquid line filter so I have then added 1 more oz to account for this--the total charge is about 13 oz.

    I have had a number of problems with the unit, most of which have been fixed now. The last being a restricted cap tube. I cut off the first 2" of the cap tube and this fixed the restriction. My high side pressure is running about 125 PSI, the low side about 0 PSI. The compressor is running about 6 amps, the RLA value. I may be a little low on charge--I haven't added more for the reason below.

    When I operate the freezer and the freezer cabinet is close to its set temperature (1 degree F) my suction line temperature seems to oscillate with a pretty high amplitude. I have attached a pdf file with a chart of the oscillation. I am thinking that if I add more refrigerant, the oscillations will get larger and I may return liquid back to the compressor--so I am hesitant to do this.

    I have taped the cap tube to the suction line for most of the suction line length (50"). The suction line and the cap tube are inside an insulated sleeve. I did this with the idea of precooling the refrigerant before it hits the evaporator. I am wondering if this thermal connection may be causing my oscillation.

    Has anyone seen this sort of thing before?

    Thanks,
    Greg Laird



  2. #2
    glaird's Avatar
    glaird Guest

    Re: Oscillating Suction Line Temperature

    My attachment didn't upload on the first post. It is here.
    Attached Files Attached Files

  3. #3
    royalchiller's Avatar
    royalchiller Guest

    Re: Oscillating Suction Line Temperature

    I know this may seem stupid, but, are you sure you fluke clamp-on isn't having problems? I've found that fluke thermistors tend to fluctuate when they get old. Just a thought.

  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Oscillating Suction Line Temperature

    Glaird, i've not used MP66 but would you consider a different refrigerant and compare the results?

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Oscillating Suction Line Temperature

    Assuming the suction line temp measurement is near the compressor inlet, it seems a little overcharged to me.

  6. #6
    Join Date
    Aug 2010
    Location
    australia
    Posts
    15
    Rep Power
    0

    Re: Oscillating Suction Line Temperature

    what is the ambient temprature/ air onto condensor and did u change the oil from mineral to alkylbenzene at the time of retrofit?


  7. #7
    after5HVAC's Avatar
    after5HVAC Guest

    Re: Oscillating Suction Line Temperature

    Did you find the trouble? I'm having the same problem with a Goodman A/C where the suction line temp. varies from 50 to 63 deg. every 6 to 7 minutes.

    Thanks

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Oscillating Suction Line Temperature

    Quote Originally Posted by after5HVAC View Post
    Did you find the trouble? I'm having the same problem with a Goodman A/C where the suction line temp. varies from 50 to 63 deg. every 6 to 7 minutes.

    Thanks
    Is it TXV or capilary/fixed orifice system?

  9. #9
    after5HVAC's Avatar
    after5HVAC Guest

    Re: Oscillating Suction Line Temperature

    On the parts list the metering device is called a "flowrater". I think that is a fixed orifice

Similar Threads

  1. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  2. High Liquid Line Temperature
    By airefresco in forum Commercial
    Replies: 37
    Last Post: 11-02-2009, 04:36 PM
  3. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  4. Bearing trouble - rotary compressor
    By rosetennis in forum Industrial Compressors
    Replies: 6
    Last Post: 18-05-2006, 01:26 AM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •