Oscillating Suction Line Temperature
Hello,
I have a 1500 BTU freezer in an Ice Cream Vending Machine that I am repairing. The unit was originally an R12 unit that I have converted to MP66. It was not working when I started the repair work and I have no idea what the correct R12 high side and low side pressures were. The unit label states that the charge should be 15 Oz of R12. I have taken 80% of this value (MP66 adjustment) leaving a 12 Oz MP66 charge. I have added a larger liquid line filter so I have then added 1 more oz to account for this--the total charge is about 13 oz.
I have had a number of problems with the unit, most of which have been fixed now. The last being a restricted cap tube. I cut off the first 2" of the cap tube and this fixed the restriction. My high side pressure is running about 125 PSI, the low side about 0 PSI. The compressor is running about 6 amps, the RLA value. I may be a little low on charge--I haven't added more for the reason below.
When I operate the freezer and the freezer cabinet is close to its set temperature (1 degree F) my suction line temperature seems to oscillate with a pretty high amplitude. I have attached a pdf file with a chart of the oscillation. I am thinking that if I add more refrigerant, the oscillations will get larger and I may return liquid back to the compressor--so I am hesitant to do this.
I have taped the cap tube to the suction line for most of the suction line length (50"). The suction line and the cap tube are inside an insulated sleeve. I did this with the idea of precooling the refrigerant before it hits the evaporator. I am wondering if this thermal connection may be causing my oscillation.
Has anyone seen this sort of thing before?
Thanks,
Greg Laird
-
27-07-2010, 06:01 PM #2
Re: Oscillating Suction Line Temperature
My attachment didn't upload on the first post. It is here.
-
06-08-2010, 11:44 PM #3
Re: Oscillating Suction Line Temperature
I know this may seem stupid, but, are you sure you fluke clamp-on isn't having problems? I've found that fluke thermistors tend to fluctuate when they get old. Just a thought.
-
07-08-2010, 04:19 AM #4
Re: Oscillating Suction Line Temperature
Glaird, i've not used MP66 but would you consider a different refrigerant and compare the results?
-
07-08-2010, 06:37 AM #5
Re: Oscillating Suction Line Temperature
Assuming the suction line temp measurement is near the compressor inlet, it seems a little overcharged to me.
-
09-08-2010, 12:38 PM #6
Re: Oscillating Suction Line Temperature
what is the ambient temprature/ air onto condensor and did u change the oil from mineral to alkylbenzene at the time of retrofit?
-
16-08-2010, 02:13 PM #7
Re: Oscillating Suction Line Temperature
Did you find the trouble? I'm having the same problem with a Goodman A/C where the suction line temp. varies from 50 to 63 deg. every 6 to 7 minutes.
Thanks
-
16-08-2010, 02:25 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
16-08-2010, 03:02 PM #9
Re: Oscillating Suction Line Temperature
On the parts list the metering device is called a "flowrater". I think that is a fixed orifice
Similar Threads
-
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
High Liquid Line Temperature
By airefresco in forum CommercialReplies: 37Last Post: 11-02-2009, 04:36 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
Bearing trouble - rotary compressor
By rosetennis in forum Industrial CompressorsReplies: 6Last Post: 18-05-2006, 01:26 AM -
Minimal required R134a speed in suction line
By DaBit in forum CPU OverclockersReplies: 32Last Post: 08-05-2002, 05:19 AM