    copeland compressor



    I recently installed a copeland compresso 5ton, replaced capacitor got gas in the system but the compressor won't start. The condenser fan starts up but nothing? Any suggestions, contactor is brand new and it doesn't have a low pressure switch reset



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: copeland compressor

    Have you tried hp switch? are you getting voltage to your contactor coil? are the compressor fuses/overloads ok? is the unit setpoint low enough for the unit to run? what type of kit is the compressor on

  3. #3
    Join Date
    Jul 2009
    Location
    miami, fl
    Posts
    10
    Rep Power
    0

    Re: copeland compressor

    I thought about the hp switch but couldn't find one on the condenser unit. I am getting line voltage, then I turned the thermostat to cool my contactor pulls in. I am getting power through the contactor for a few seconds then it goes away. I put my ammeter to see if I was getting enough amps and noticed it was 2 or 3 amps below what is stamped on the compressor. There are no control relays on the condensing unit
    just a capacitor and a contactor. That's why I'm confussed because there is really not too much to look for. Any suggestions would be appreciated

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: copeland compressor

    Does the power stay on at the line in of the contactor if it does and you lose voltage on the load side with the coil pulled in i'd replace the contactor i know you said it was new but these things happen

  5. #5
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: copeland compressor

    PS is the compressor capacitance start or capacitance run? is ther any compressor protection modules robert shaws etc

  6. #6
    Join Date
    Aug 2010
    Location
    Brisbane
    Age
    39
    Posts
    7
    Rep Power
    0

    Re: copeland compressor

    are you getting voltage through the contactor and to the compressor? i would check voltage through contactor then at compressor, check capacitor again and check wiring is correct, is the compressor hot, could be an internal thermal overload either faulty or if it is hot it could be tripped!!

  7. #7
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: copeland compressor

    My bets on a faulty contactor.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  8. #8
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: copeland compressor

    If the compressor is a single phase one it would do such proplems if the power cables are poorly selected or if the voltage is under the compressor rated voltage put a powerpack (supco or equivalent) to give the compressor a hard start.
    I beleive that in your case the compressor pull of current while starting is decreasing the line voltage , those making the contactors relay deactivated.
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: copeland compressor

    Hello Botrous, nice to see you again here.


    tcdmtcdt,
    5 ton compressor single phase??
    Will you please give us the model?

    Maybe that the capacitor belongs to the fan motor?

    If the compressor and fan are on the same circuit and the compressor is trying to start, the fan will hardly turn as the tension will drop.

  10. #10
    Join Date
    Jul 2010
    Location
    Ireland
    Posts
    3
    Rep Power
    0

    Re: copeland compressor

    what model of copeland compressor do you have? as Botrous said a start pack may be required. all copelands single phase should be fitted with a start pack,if the comp. is a recip. you definitely need a start pack. Have you line voltage at the compressor terminals. Possibility that copeland wiring ex factory a problem I have seen it happen on two occasions.