    need your help



    Running an air cooled water chiller with two reciprocating compressors and R22 *****
    get the followig
    first circuit - full load:
    - Ambient temp: 29 C
    - lvg evap water temp: 6.5 C
    - sat evap temp: -2 C
    - Sat cond temp: 50 C
    - Superheat: 5 C
    - Subcool: 10 C
    - Discharge temp: 88 C

    Second circuit - full load:
    - Ambient temp: 29 C
    - lvg evap water temp: 6.5 C
    - sat evap temp: 0 C
    - Sat cond temp: 50 C
    - Superheat: 5 C
    - Subcool: 10 C
    - Discharge temp: 76 C

    * is sat evap temp low for cir-1?
    * is disch temp high for cir-1?
    * is subcool high for both cir
    * is evap approach and cond approach high for both cir.

    thank you



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: need your help

    Hi Sharif,

    What is the entering water temp?

    Can you give the pressures as well,


    Chemi

  3. #3
    Join Date
    May 2005
    Location
    Syria
    Age
    53
    Posts
    7
    Rep Power
    0

    Re: need your help

    Hi Chemi;

    - entering water temperature for both circuits = 12.5 to 13 C
    - Cond pressure for both circuits = 18.5 to 19 bar
    - evap sat press cir-1 = 4.3 bar
    - evap sat press cir-2 = 5 bar

    Thank you

  4. #4
    Join Date
    Jun 2005
    Location
    Madison
    Age
    61
    Posts
    32
    Rep Power
    0

    Re: need your help

    When I design an air cooled chiller with plate evaporator, normally the condensing temperature is 25F higher than ambient temperature, and the evaporating temperature is 10F lower than outlet water temperature. Although I cannot prove it, I feel under these conditions, the system is price efficient. If I were you, I would select evaporating temperature = 0 C and the condensing temperature = 43 C ~ 45 C. Please let me know if anyone has good ideas to select condensing and evaporating temperatures.

    Under the condition the evaporating temperature is 0 C, condensing temperature is 45 C, 10 C subcooling, 5 C superheat, compressor isentropic efficiency is 0.7, no pressure losses in suction line and discharge line, no compressor heat loss, and no suction line unuseful superheat, the discharge temperature should be 68.4 C.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need your help

    On the condensers, what are the entering and leaving air temperatures?
    Last edited by Gary; 05-08-2005 at 04:51 PM.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: need your help

    Hi Gary,

    its easy to find the answer to your question,

    normally the condensing temperature is 25F higher than ambient temperature,
    Dont you think?

    Chemi

  7. #7
    Join Date
    Nov 2004
    Location
    Sri Lanka
    Age
    77
    Posts
    18
    Rep Power
    0

    Re: need your help

    Quote Originally Posted by shsalameh
    Running an air cooled water chiller with two reciprocating compressors and R22 *****
    get the followig
    first circuit - full load:
    - Ambient temp: 29 C
    - lvg evap water temp: 6.5 C
    - sat evap temp: -2 C
    - Sat cond temp: 50 C
    - Superheat: 5 C
    - Subcool: 10 C
    - Discharge temp: 88 C

    Second circuit - full load:
    - Ambient temp: 29 C
    - lvg evap water temp: 6.5 C
    - sat evap temp: 0 C
    - Sat cond temp: 50 C
    - Superheat: 5 C
    - Subcool: 10 C
    - Discharge temp: 76 C

    * is sat evap temp low for cir-1?
    * is disch temp high for cir-1?
    * is subcool high for both cir
    * is evap approach and cond approach high for both cir.

    thank you
    DEAR SHSALAMEH

    bE CAREFUL YOUR CHILLER IS REACHING THE DANGER ZONES TOO CLOSE TO FREEZING.Cooler approaches are not good enough, suction low discharge temperatures too high.

    patrickj

  8. #8
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: need your help

    from the data,the evap temp is lower. I'm not sure if you add anti-freezing liquid in the water. I think the evap temp should be around 2C. Verify the water volume and check the ampere of the compressor to see if the charge is a little less which may increase the dischange temp? only for your ref.

    lichuan

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need your help

    Quote Originally Posted by chemi-cool
    Hi Gary,

    its easy to find the answer to your question,


    Dont you think?

    Chemi
    Enlighten me.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: need your help

    I'm wondering if the evaporators are counterflow as they should be, or parallel flow, as they appear to be not picking up a full heat load and are showing a high approach temperature.

    On the other hand, the condensers appear not to be able to handle the heat load they currently have, much less a full heat load.
    Last edited by Gary; 06-08-2005 at 08:13 AM.