    Panasonic Multisplit



    Hi guys, installed a Panasonic Inverter Multisplit 3 indoor units approx 18 months ago, a problem has arose, the system runs for about 5 mins with no cooling. LED 1 and 3 on outdoor unit is on and this is relating to high discharge pressure. The suction pressure is running at 2 bar and the liquid line pressure is showing 18 bar and yet the indoor units are not showing a fault by the timer light.

    Can anyone shed some light.

    Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Panasonic Multisplit

    From your symptoms, I would say that a high discharge pressure and low suction pressure (starved evaporator) it seems that you may have a slight blockage.

    are the expansion valves (eev's) opening correctly? or more likely, it is a common problem before the eev's (blockage) as all of the indoor units are doing the same.

  3. #3
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    17

    Re: Panasonic Multisplit

    Hi Frank thanks for your input, yes it does seem to be a blockage of some sort as all units are not cooling and the EEVīs are making quite a noise, not sure if they are closed when trying to cool.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Panasonic Multisplit

    You need to use a touch probe thermometer around the outdoor unit piping to locate it if it doesn't run long enough to start frosting or doesn't cause frosting at all.

    It will certainly show as a rapid temp drop with the probe though

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Panasonic Multisplit

    Is this high pressure or high discharge temperature, 18bar doesn't seem that high for R410A, i think they usually trip around 40bar! (but could be wrong)
    If its high discharge temp, it could be short of refrigerant, so i'd be weighing it out to see if it has the correct charge.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Panasonic Multisplit

    Good point MS

    It's always difficult to pinpoint the cause when you are not working on the system as certain symptoms can look like one thing but end up being something completely different
    Last edited by frank; 23-07-2010 at 08:13 PM.

  7. #7
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    17

    Re: Panasonic Multisplit

    Hi Frank and MS would you have a high side pressure of 18Bar (Which is not that high, it is almost normal), when you have a suction pressure of low side pressure of 2Bar

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Panasonic Multisplit

    As MS says, it would be a good idea to check your gas charge first

Similar Threads

  1. Help with Panasonic units please
    By dazdidge in forum Air Conditioning
    Replies: 4
    Last Post: 09-09-2009, 07:07 AM
  2. Panasonic Spares
    By willetts in forum Air Conditioning
    Replies: 3
    Last Post: 27-08-2009, 02:38 PM
  3. Panasonic Urban rebadged Daikin
    By complete HVAC in forum Air Conditioning
    Replies: 0
    Last Post: 19-08-2009, 04:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •