22-07-2010, 10:51 PM #1
409a meat case issue
I am new to this sight and need some help. I am a first year tech so this site is great for me. I was at a job and found a leak on a meat case with 409a in it. I repaired the leak, pullled a vaccuum down to 360 microns so I know the leak is fixed. I just dont know what pressures I should be looking for on high and low side. It has about fifteen feet of line set and has a gravity cooled evap, no evap fans, one on bottom of case and one on top. What should my subcooling be? Or should I say what should evap temp be? please help, thx
-
27-07-2010, 05:30 AM #2
Re: 409a meat case issue
Hello Mate,
What are you really asking? are you worried about your refrigerant charge? Do you have a TXV or is it capillary?
R-409A has properties and performance similar to R-12, Low side pressures are similar to those of R-12, while high side pressures will typically be 15 to 25 psi(1-1.7bar) higher
Iv personally never seen a meat case with static Evaporators, but i guess they would dry the meat out less.
If your running Static Evaps and not forced draft(fans) id get hold of a Pressure/temp chart for R12 and relate what pressures you are running to what it says on the chart.
Id expect your suction pressure to be pretty low, possibly around 10-15 psi(0.7-1 bar).
-
27-07-2010, 08:13 PM #3
Re: 409a meat case issue
spot on licencetochill or if you are very much a newbeeeee r12 and r134a very similar
-
27-07-2010, 09:59 PM #4
Re: 409a meat case issue
You say that the leak is fixed because you did a vacuum test.
OK so it held at a pressure of +14psi, did you do a pressure test as well?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
27-07-2010, 11:09 PM #5
Re: 409a meat case issue
what sort of case is it,does it not have a label with make,model etc,if so it should give you a gas charge,just weigh it in and away you go.
-
28-07-2010, 12:08 AM #6
Re: 409a meat case issue
yes i put 150 lbs of nitro in system and held for an hour with no drop at all. I got it to work on saturday, and so far so good. It had a reading of 15 psi on low side which is working out great, the meat case is staying between 35-41. Thank you for the reply, i appreciate it
Similar Threads
-
Daikin output overcurrent issue
By wilson77 in forum Air ConditioningReplies: 15Last Post: 18-01-2010, 11:36 PM -
Having some island meat case issues.
By Supertech87 in forum Supermarket RefrigerationReplies: 2Last Post: 17-04-2009, 12:59 PM -
Flood back issue?
By Arc in forum Trouble ShootingReplies: 15Last Post: 28-10-2008, 03:40 PM -
kys0r/warren produce case not cold enough
By shawn626 in forum CommercialReplies: 5Last Post: 28-09-2008, 02:52 PM -
cpc case controller
By dingo in forum Trouble ShootingReplies: 4Last Post: 09-04-2008, 09:35 AM