    409a meat case issue



    I am new to this sight and need some help. I am a first year tech so this site is great for me. I was at a job and found a leak on a meat case with 409a in it. I repaired the leak, pullled a vaccuum down to 360 microns so I know the leak is fixed. I just dont know what pressures I should be looking for on high and low side. It has about fifteen feet of line set and has a gravity cooled evap, no evap fans, one on bottom of case and one on top. What should my subcooling be? Or should I say what should evap temp be? please help, thx



  2. #2
    Join Date
    Jan 2007
    Location
    New Zealand
    Age
    42
    Posts
    50
    Rep Power
    18

    Re: 409a meat case issue

    Hello Mate,
    What are you really asking? are you worried about your refrigerant charge? Do you have a TXV or is it capillary?

    R-409A has properties and performance similar to R-12, Low side pressures are similar to those of R-12, while high side pressures will typically be 15 to 25 psi(1-1.7bar) higher

    Iv personally never seen a meat case with static Evaporators, but i guess they would dry the meat out less.

    If your running Static Evaps and not forced draft(fans) id get hold of a Pressure/temp chart for R12 and relate what pressures you are running to what it says on the chart.
    Id expect your suction pressure to be pretty low, possibly around 10-15 psi(0.7-1 bar).

  3. #3
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: 409a meat case issue

    spot on licencetochill or if you are very much a newbeeeee r12 and r134a very similar

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 409a meat case issue

    You say that the leak is fixed because you did a vacuum test.

    OK so it held at a pressure of +14psi, did you do a pressure test as well?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: 409a meat case issue

    what sort of case is it,does it not have a label with make,model etc,if so it should give you a gas charge,just weigh it in and away you go.

  6. #6
    Join Date
    Jul 2010
    Location
    new jersey
    Posts
    5
    Rep Power
    0

    Re: 409a meat case issue

    yes i put 150 lbs of nitro in system and held for an hour with no drop at all. I got it to work on saturday, and so far so good. It had a reading of 15 psi on low side which is working out great, the meat case is staying between 35-41. Thank you for the reply, i appreciate it

Similar Threads

  1. Daikin output overcurrent issue
    By wilson77 in forum Air Conditioning
    Replies: 15
    Last Post: 18-01-2010, 11:36 PM
  2. Having some island meat case issues.
    By Supertech87 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 17-04-2009, 12:59 PM
  3. Flood back issue?
    By Arc in forum Trouble Shooting
    Replies: 15
    Last Post: 28-10-2008, 03:40 PM
  4. kys0r/warren produce case not cold enough
    By shawn626 in forum Commercial
    Replies: 5
    Last Post: 28-09-2008, 02:52 PM
  5. cpc case controller
    By dingo in forum Trouble Shooting
    Replies: 4
    Last Post: 09-04-2008, 09:35 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •