Results 1 to 41 of 41
    Mexico
    44
    158
    Solenoid Valves in Parallel Compressors Rack System
    Hello everyone!
    When using a Parallel Compressors Rack System for several rooms at different temperatures I have seen EPR's (1 for each room) installed just before the rack's suction manifold to mantain the different room's pressures, and I have seen that Solenoid Valves are installed just after the liquid manifold (1 for each room) to cut refrigerant flow when set temperature is reached or when defrost is required.
    Doesn't the EPR's should be enough to control temperature? Is it necessary to use Solenoid Valves?
    Thanks in advanced!
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Solenoid Valves in Parallel Compressors Rack System
    EPR is used to maintain a certain pressure\ temp in the evaporator.
    SV will close when the room have reached the desired temp.
    Mexico
    44
    158
    Thanks chemi-cool.
    Do you use to put SV at the Rack or at the Evaporator??
    One thing I noticed is that when big diameter pipes are used it "hits" really strong when SV opens and liquid start to flow.
    Oct 2003
    5,630
    If you install a SV far from the TEV, you can brake the TEV due to liquid hammer.
    You have to install the SV as close as possible to the TEV.
    Installing all the SV's in the machineroom is a very bad practice.
    Jun 2007
    Sri Lanka
    88
    Thank you Peter_1. I will redesign all my equipments & install the SV close to the TEV. After long period of time the TEV is not working properly. So we had to replace them after some time.
    Mexico
    44
    158
    Thanks Peter_1, that's what I though.
    Regarding to the use of EPR's, somebody told me there was no need to cut flow off with the SV because the EPR would manage to keep the room at required temperature, Is that possible?
    Oct 2003
    5,630
    Georgedvf, you need and an EPR and a SV in a 'normal application'
    The EPR will prevent too cold draft blowing from the evaporator where the SV maintains the room temperature.
    You can regulate room temperature with the EPR but you then need and EPR which adapts its evaporating temperature according to the room temperature.Danfoss has a special valve for this http://www.ra.danfoss.com/TechnicalI...OPC320A122.pdf That's in fact a little bit what a VRV/VRF airco is doing. Adapting mean coil temperature to the room temperature.
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by georgedvf View Post
    George, if you don't use SV you could control the room temperature by switching on/off the aircoolers fans...however there is a big big risk/probability that you flood the suction line manifold and the compressor with liquid .
    Sep 2003
    ISRAEL
    72
    4,248
    Quote Originally Posted by Sandro Baptista View Post
    Bad advice my friend, very bad.
    Jan 2010
    Christchurch
    54
    28
    We had a problem with large liquid lines hammering when the solenoid valve opened, moving the solenoid to the evap can be a huge job, what we did was install a small 1/4 inch solenoid which opened first around the larger solenoid, this filled the larger liquid line then opened the large solenoid after a preset time
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by Paul J View Post
    Yes, that's right
    Mar 2006
    Merate (LC) - Italy
    2,549
    This is a typically wrong application, with legacy components and inherited operation from jurassic experience.
    If one wants to control a room temperature, for what good dam reason does one control the suction pressure? Wouldn't it be more logic to control the room temperature and cycle on that?
    EPRs would be useless (superheating regulated per room) and SV would only be needed to stop liquid feeding TEVs for the rooms already at set. And to prevent hammering, just stop pumping down.
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by chemi-cool View Post
    Chemi,
    I didn't said that's a good solution, by contrary is very risky
    Quote Originally Posted by NoNickName View Post
    The room temperature it would not be controled by suction pressure. A thermostat it would be used but instead acting on the solenoid valve on/off it would act on the fans.
    Mexico
    44
    158
    NoNickName, I didn't understand the last part about prevent hammering stopping pump down. Since I'm talking about a Parallel Compressors Rack for several rooms.
    Can you tell me more about what would be a "New age" control solution for this kind of systems? Where can I find info?
    Mar 2006
    Merate (LC) - Italy
    2,549
    Yes, this is typical compressor pack / multiplex system. When the last of compressors stop, it is a common practice to stop it on a low pressure switch. This is referred as pump down procedure. At restart, when the SV opens, refrigerant fills up the vacuum created by the pump down, and the result is liquid hammering.
    Register yourself and download the programmable controllers brochure form www.dixell.it . You can have a slight glance of the new ideas for the refrigeration sector
    Mexico
    44
    158
    Ok, but when there's several rooms and only one room stops it's the same hammering and no compressor stops, so no pump down is happening there, right? I think the only solution for this is to install the SV near the TEV...
    Thanks for that link, I will look into it.
    Mexico
    44
    158
    Just to get it right, so when using Parallel Compressors Rack and several rooms yo DO use SV neear as possible from the TEV to stop refrigeratn flow when set temperature is reached or defrost is required, right??
    Oct 2003
    5,630
    ...At restart, when the SV opens, refrigerant fills up the vacuum created by the pump down, and the result is liquid hammering.....
    Not if teh SV is mounted just in front of the TEV.
    Carrefour , Colruyt and Delhaize, big Belgium supermarkets describe in their manuals you have to install the SV's as close as possible to the TEV.
    Mar 2006
    Merate (LC) - Italy
    2,549
    It doesn't matter. It probably is worse when the SV is near the TEV. Same hammering in less volume.
    Oct 2003
    5,630
    If one wants to control a room temperature, for what good dam reason does one control the suction pressure? ...
    When cold rooms (0°C) an processing rooms are connected to the same pack which is often the case, evaporating at -10°C, then an EPR could prevent icing up the coils in the processing rooms, or increase latent heat of the blown air so that there are less cold draft complaints from peoples working in those rooms or an EPR could be used to increase RH an a central manifold.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Which is also wrong. When ventilation stops, air stratifies.
    Dec 2008
    Portugal
    48
    1,020
    And what's the problem of that?
  23. #23
    Mar 2006
    Merate (LC) - Italy
    2,549
    The temperature probe does not fully reflect the room temperature, which changes along the vertical profile.
    If you've got food along vertical racks, it may not be properly refrigerated when stacked at high level, or may be too cold at low levels for fresh produce like lettuce or fruits.
  24. #24
    Dec 2008
    Portugal
    48
    1,020
    1st » When the aircooler is working (because the temperature is higher than the set-point) every thing is okay, right? the ventilation ensure the air circulation.
    2nd » When the fans stops I understand that the a "cooled" air flow will down. But this will be a very little refrigeration effect when compared with "static aircooler" (natural convection / no fans).
  25. #25
    Mar 2006
    Merate (LC) - Italy
    2,549
    I'm only saying that if air settles and statifies, the warm air will rise, and the cold air will sink. This is also known as convection.
    It has nothing to do with refrigeration.
  26. #26
    Dec 2008
    Portugal
    48
    1,020
    okay man...I just still can see what's the problem of that.
    That's a good debate
  27. #27
    Mar 2006
    Merate (LC) - Italy
    2,549
    Ok, if warm air rises, the goods stocked at high level will be warmer than the goods at low levels.
    The quality of some goods require strict temperature control, for example lettuce and fresh produce, flowers, bananas....
    Imagine a mushroom growing chamber. You would expect different growing rates from warmer to colder shelves.
  28. #28
    Dec 2008
    Portugal
    48
    1,020
    Okay...put the probe on the higher part (higher temperature as it should be)...but like I have told you we are talking about an aircooler that is not for natural convection so the aircooler capacity with the fans off will be very smaller and this effect would not be notice.
    Maybe we are running away a little of this thread, don't you think?
  29. #29
    Mar 2006
    Merate (LC) - Italy
    2,549
    I think you don't understand. If I put the probe at higher level, the temperature on the floor would be even colder.
    I know it is an aircooler, BUT WHEN THE FANS ARE OFF, NATURAL CONVECTION HAPPENS, BELIEVE IT OR NOT, YOU WANT IT OR NOT.
  30. #30
    Dec 2008
    Portugal
    48
    1,020
    Hey chill out man. I understand it will be cooler on floor...but I just say that effect will be smaller for this air forced cooler...and besides that the cold air will heat exchange with the products and air at the neighbourdhood so when it reaches the floor the temperature will not be so different to create a big deal.
    This is my opinion, that's all.
  31. #31
    Mar 2009
    ireland
    87
    i'm with sv at exp vlv...... or just to throw a right spanner use danfoss elect vlv's should i duck now
  32. #32
    Mar 2006
    Merate (LC) - Italy
    2,549
    Again, mileage may vary. Loss of goods is always the case when no backup and no spare parts are available. Blame is put on the producer of the equipment, as always.
    I got a court case, because a close control unit went down and the server room of a bank stopped. They were transacting 1millionGBP per second. They had a loss of few billion GBP, all because of a 5 years old fan that burnt and no spares on site.
    They got kicked and ashamed by the judge.
    If you want to avoid hammering between the SV and the TEV, put the drier in between.
  33. #33
    Oct 2003
    5,630
    Came the judge to that decision without appointing first a judicial expert?
    Putting the drier between SV and TEV, that need some clarification because the drier has almost no volume where velocity can decrease and avoid pressure build up
  34. #34
    Mar 2006
    Merate (LC) - Italy
    2,549
    The judge refused the case and didn't appoint any expert.
    It depends on the drier. There are driers with plenty of volume inside. Anyway the core is able to slow the hammer, I think.
  35. #35
    Oct 2003
    5,630
    In Belgium, a judge can't refuse a case, this is against the defense of whom who started the case.
    There has to be anyhow a case with lawyers, eventually without the appointment of a judicial expert. But I'm sure, both parties (defended/offended) can give statements/arguments which justify that and why they're right and why the other was wrong.
  36. #36
    Mar 2006
    Merate (LC) - Italy
    2,549
    This is singular. What if a case is clearly unfounded?
    Do they have so much money and time in Belgium?
    In Italy, he is called GUP (judge of preliminary hearing).
    E.g. there had been a case of a terminally ill man who refused being treated. The hospital wanted him to be forcefully treated (to avoid him self killing) and called him in judgement. The GUP refused the case because everybody is free to take or refuse medicines upon his/her only free will, which is a Constitutional Right.
    But this is clearly off topic here.
  37. #37
    Oct 2003
    5,630
    I...
    It has nothing to do with money nor time but about legal rights. How can a judge class a case as unfounded if the problem relates to a technical matter? He can't know all the details to do this, especially the technical ones to make the right decision.
    It's also complete unthinkable that politicians can interfere or change laws that put them outside that law. Especially if there are presumptions that a politician broke the law. The politician will then temporarily placed outside his/her political immunity.
    Law and politics are clearly separated here.
  38. #38
    Mexico
    44
    158
    Thanks to all.
    I have one more question.
    What would happen if no SV's are used and only EPR's are installed?
    What happens to rooms temperatures?
    What happens when defrost is needed?
    Ok, there was three more questions....
    Thanks!
  39. #39
    May 2006
    India
    399
    FURTHER INPUT ON THIS SYSTEM :
    1) THE LOAD OF THE LOWEST TEMP EVAP SHOULD BE AT LEAST 60% OF THE TOTAL LOAD .
    2) HIGH TEMP EVAP SHOULD HAVE EPRs
    3) LOW TEMP EVAP SHOULD HAVE A CHECK VALVE IN SUCTION LINE .
    4) SOL VALVES FOR EACH EVAP NEAR TO TEX VALVE AS DISCUSSED IN THIS THREAD BY VARIOUS CONTRIBUTORS
  1. Daikin fault codes
  2. Pump down system, solenoid valve
    By AleksanderNH in forum Fundamentals
    Last Post: 10-06-2010, 12:07 AM
  3. Parallel oil system problem
    By Tom C in forum Technical Discussions
    Last Post: 04-06-2010, 12:19 AM
  4. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Last Post: 27-01-2009, 10:36 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Last Post: 30-12-2003, 01:33 PM