    Daikin VRV-S switching off



    I have a VRV-S with four indoor FXSQ air handlers and one BRC1D** wired remote controller.

    Over the last day I have found twice that the controller is switched off (no red light next to On/Off button). Both times when I turned it back on the system started immediately and no fault codes were showing.

    No one has turned it off so what might be causing this to happen?

    Thank you.



  2. #2
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Daikin VRV-S switching off

    Quote Originally Posted by mchild View Post
    I have a VRV-S with four indoor FXSQ air handlers and one BRC1D** wired remote controller.

    Over the last day I have found twice that the controller is switched off (no red light next to On/Off button). Both times when I turned it back on the system started immediately and no fault codes were showing.

    No one has turned it off so what might be causing this to happen?

    Thank you.

    Check to see if any time clock programs are registered and if the the timer is enabled (clock icon bottom left of BRC1D control)

  3. #3
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S switching off

    Quote Originally Posted by AbsoluteWDJ View Post
    Check to see if any time clock programs are registered and if the the timer is enabled (clock icon bottom left of BRC1D control)

    Thanks for the quick response, but no programs or schedules are running. Same temp all the time.

    This has just started to happen in the last 24 hours. Before that the controller had not been touched in weeks.

  4. #4
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S switching off

    I have it sorted out.

    The installer placed switches connected to T1 and T2 in case of condensate not draining properly. Good news is I did not have water pouring out of my attic and I figured it out before too long. I have now placed a reminder next to the controller for the next time this happens. Plus, I must perform the required maintenance to keep them from properly draining.

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin VRV-S switching off

    you should wire the high limit stat on the condensate pump to X15A or put it in series with the existing high limit stat then the system will come up with an A3 fault which means there is a high limit alarm on your condensate pump..

  6. #6
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S switching off

    Quote Originally Posted by brunstar View Post
    you should wire the high limit stat on the condensate pump to X15A or put it in series with the existing high limit stat then the system will come up with an A3 fault which means there is a high limit alarm on your condensate pump..

    Good suggestion. If that had been done it would have taken me to the issue straight away.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •