Thread: Daikin VRV-S switching off
-
22-07-2010, 04:39 PM #1
Daikin VRV-S switching off
I have a VRV-S with four indoor FXSQ air handlers and one BRC1D** wired remote controller.
Over the last day I have found twice that the controller is switched off (no red light next to On/Off button). Both times when I turned it back on the system started immediately and no fault codes were showing.
No one has turned it off so what might be causing this to happen?
Thank you.
-
22-07-2010, 04:42 PM #2
-
22-07-2010, 04:48 PM #3
-
22-07-2010, 10:20 PM #4
Re: Daikin VRV-S switching off
I have it sorted out.
The installer placed switches connected to T1 and T2 in case of condensate not draining properly. Good news is I did not have water pouring out of my attic and I figured it out before too long. I have now placed a reminder next to the controller for the next time this happens. Plus, I must perform the required maintenance to keep them from properly draining.
-
22-07-2010, 11:39 PM #5
Re: Daikin VRV-S switching off
you should wire the high limit stat on the condensate pump to X15A or put it in series with the existing high limit stat then the system will come up with an A3 fault which means there is a high limit alarm on your condensate pump..
-
23-07-2010, 12:37 AM #6
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Mitsi City Multi VS Daikin VRV
By sumsor in forum FundamentalsReplies: 5Last Post: 14-07-2010, 05:54 PM -
Daikin AC parts from UK
By skel00 in forum Air ConditioningReplies: 5Last Post: 05-04-2009, 01:24 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM -
Getting a price from Daikin....
By monkey spanners in forum Chit Chat & Service StoriesReplies: 4Last Post: 17-08-2008, 09:46 PM