Results 1 to 3 of 3
  1. #1
    hwebb54's Avatar
    hwebb54 Guest

    hussman door icecream freezer issues



    I'm working on a 20 door run of hussman glass door freezers that will not get cold enough. Suction line pressure seems high to me. I'm going to give u guys some stats and see in you can help.

    Low side 25 (-10)
    High side 280(115)
    Temp in cooler 3.6
    Suction line temp at txv bulb 6.6
    Liquid line temp 106 in compressor room.
    Compressor room temp. 100-106
    This is a 404a system with a 7.6 Copeland compressor.

    Any thoughts would be appreciated.



  2. #2
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: hussman door icecream freezer issues

    Quote Originally Posted by hwebb54 View Post
    I'm working on a 20 door run of hussman glass door freezers that will not get cold enough. Suction line pressure seems high to me. I'm going to give u guys some stats and see in you can help.

    Low side 25 (-10)
    High side 280(115)
    Temp in cooler 3.6
    Suction line temp at txv bulb 6.6
    Liquid line temp 106 in compressor room.
    Compressor room temp. 100-106
    This is a 404a system with a 7.6 Copeland compressor.

    Any thoughts would be appreciated.
    Hi, hwebb54. You are on the edge, but you should be able to improve things. Your superheat is too high @ 16.6 deg F or C. Set your superheat at 5 deg F. This will tend to increase your suction pressure, but overnight, you should see an improvement in temperatures. Also, make sure you only have a single defrost per day.

  3. #3
    hwebb54's Avatar
    hwebb54 Guest

    Re: hussman door icecream freezer issues

    Thank you for the info. I'll get back to you with the results.

Similar Threads

  1. Replies: 5
    Last Post: 10-03-2011, 03:58 PM
  2. 3-door Hussman freezer - High head?
    By W.ma.RefrigTech in forum Trouble Shooting
    Replies: 3
    Last Post: 21-03-2010, 09:32 AM
  3. Need help quick with walk-in freezer issues!
    By hysiderafter in forum Commercial
    Replies: 5
    Last Post: 12-12-2007, 12:57 AM
  4. Blast freezer related issues ~~
    By spiderman in forum Fundamentals
    Replies: 5
    Last Post: 24-05-2007, 07:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •