    Split Blockages



    I have to go and look at a Mitsubishi MUH-C18TV which may have blockages. Is it probable that they are only in the capillaries and does anyone have a good way of checking flows through splits as there is only one schraeder port on the service valves and I want to avoid the task of chopping into pipes within the unit.

    Thanks in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Split Blockages

    Try a contact thermometer across the cap lines or restrictors, it may highlight a potential blockage
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Split Blockages

    What are the symptoms that make you think it is a blockage?

  4. #4
    Join Date
    Jan 2005
    Location
    england
    Age
    48
    Posts
    64
    Rep Power
    20

    Re: Split Blockages

    Thanks guys
    Aparantley unit has never worked properly. I have not yet seen the unit charged and running, only pressure tested,previous engineers suspected blockages in capillaries and changed all 3. Unit still does not work and was switched off . I have to investigate so I am going back to regas and test but ive a horrible feeling unit still has problems,evidence of a water leak from indoor unit-probably froze -maybe just short of gas, what do you think?

  5. #5
    complete HVAC's Avatar
    complete HVAC Guest

    Re: Split Blockages

    These units have a mesh filter just before the expansion shut off valve, un sweat the swaged joint connecting to the valve, and there you will find it, no doubt blocked with oxidation where no ofn was purged during installation of pipework.

  6. #6
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: Split Blockages

    hi
    blockage in capillary :means you find ice in capillry.
    shortage of gas :means you have low suction pressure.
    other reason make the mitsu not working proparly: contaminated oil which result in blochage/unblochage frequently
    chech the suction pr. , evaporator fan , overlook the system for oil on piping ,take sample of compressor oil

    afeef

  7. #7
    Join Date
    May 2006
    Location
    Australia
    Age
    49
    Posts
    12
    Rep Power
    0

    Re: Split Blockages

    Mabe you need to recover the gas add test points on the indoor coil and might as well add a sight glass and filter dryer to catch crap and water in the system before it blocks the expansion valve. Does it have a capilery line in the outdoor unit to meter the liquid as well? if so this could be getting blocked by ice.

Similar Threads

  1. Pressure testing for leaks on split a/c systems
    By mrchatts in forum Air Conditioning
    Replies: 46
    Last Post: 08-04-2010, 10:02 AM
  2. panasonic 3 phase split
    By mike live in forum Air Conditioning
    Replies: 18
    Last Post: 18-08-2006, 11:54 PM
  3. Replies: 8
    Last Post: 20-05-2006, 04:21 PM
  4. Cooling condenser of split with condensate from evaporator
    By smileypete in forum Air Conditioning
    Replies: 11
    Last Post: 10-07-2005, 08:21 AM
  5. LG ducted split
    By Abe in forum Air Conditioning
    Replies: 20
    Last Post: 08-06-2005, 07:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •