19-07-2010, 02:03 PM #1
Expantion valve design
I want to design a a home made cold storage, where i am using R22 for dropping -5degree temparature. Total cooling load is 225kw.I using 1 inch dia cupper tube and reciprocating compressor(suction stroke 20kg supply stroke 1kg).Can any body tell if i use capillary expantion,what should be the mimimum dia and length of the cupper tube(Both part of the capplarity will be connected to 1 inch cupper tube to complete the refrigeration cycle)and how to determine the amount of the refrigeration for this system
-
19-07-2010, 06:33 PM #2
Re: Expantion valve design
Hi
has this already been installed or something you are thinking about?
As r22 is being phased out.....
You will be better with a adjustable expansion valve (tev)
as capillary valve design is very specific and if wrong will cause issues that will be easily sorted with a adjustable valve ie you can adjust it (open or close) to meter liquid to evap coil
-
19-07-2010, 09:38 PM #3
Re: Expantion valve design
I tried using Dancap to calculate your system but as your load is excessive for a capillary system it won't do it.
Dancap max is 34000 btu/h you are looking for 768245 btu/h.
Capillary is not the way to go for that duty.Brian - Newton Abbot, Devon, UK
Retired March 2015
Similar Threads
-
LEV does not open
By Yuri B. in forum Air ConditioningReplies: 7Last Post: 19-07-2009, 02:37 PM -
Expantion Valve
By Noori in forum Air ConditioningReplies: 3Last Post: 17-07-2008, 06:49 PM -
Expantion Valve Freeze Over
By tommy658 in forum CommercialReplies: 11Last Post: 24-03-2008, 01:34 PM -
Expantion valve adjustment
By ayaz in forum Technical SpeculationsReplies: 5Last Post: 22-04-2006, 03:43 PM