Page 1 of 2 12 LastLast
Results 1 to 50 of 54
    Jul 2010
    Mombasa
    57
    52
    14
    Trane Chiller: Noisy Oil Separator
    Hi.
    Carried out an oil Change on a Trane TRA Screw compressor. Drained old oil Charged new oil 8 Ltrs as specified on Name Plate used Trane 025E oil as Specified and after starting the system the oil separator developed a new very loud whinning noise. What could be the cause of this. Please advise
    Apr 2009
    israel
    778
    Re: Trane Chiller: Noisy Oil Separator
    Quote Originally Posted by meab View Post
    Hi.
    Hi does this noise continue when comp is loaded??
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
    Jul 2010
    Mombasa
    57
    52
    14
    Yes the noise does not stop have been running the unit with the noise
    Oct 2009
    merida mexico
    54
    282
    15
    reopen the valves of oil. which model of machine is it? Oil 8lts rtaa080 is a machine?
    Mar 2006
    Merate (LC) - Italy
    2,549
    Two reasons:
    1) the oil heaters are touching together and vibrating when the compressor is running
    2) the internal baffles are coming loose and vibrating against the case.
    In the first case, you can try removing one or more heaters. In the other case, return the oil separator for repair.
    Jul 2010
    Mombasa
    57
    52
    14
    All valves open unit running but noisy
    Jul 2010
    Mombasa
    57
    52
    14
    Oil Heaters OK. may need to check the baffles as per your advise thanks
    Jul 2010
    Mombasa
    57
    52
    14
    Unit Model No RTAB 212
    Oct 2009
    merida mexico
    54
    282
    15
    low flow of oil is causing the compressor is very noisy, recover the refrigerant and verify that no lines are blocked lubrication.
    Jul 2010
    Mombasa
    57
    52
    14
    Hi have tried all the above suggestions. Carried out an oil change to another system and again the same noise has resulted. Do not understand why this should happen
    Mar 2006
    Merate (LC) - Italy
    2,549
    Did you inspect the baffles?
    Jul 2010
    Mombasa
    57
    52
    14
    Not yet checked baffles
    Although i am surprised would fresh oil effect the baffles in 2 machines,
    Mar 2006
    Merate (LC) - Italy
    2,549
    No, you should have checked the baffles before changing the oil. No effect by fresh oil. My first suggestion was to check baffles (scroll back in the thread). I still guess the cause is related to badly welded baffles.
    Auckland
    74
    3,357
    37
    Do not know the actual machine, but do they have coalessers fitted, sounds could be from that they have shifted or burst out and flapping around. Why, I would not know.
    Jul 2010
    Mombasa
    57
    52
    14
    The Units are Trane Chillers Model TRTAB 212 with 2No. Screw Compressors Model CHHN060KEN070A.
    What are Coalessers? do not know these would they have another name?
    Mar 2006
    Merate (LC) - Italy
    2,549
    Coalescer is the other name of the oil separator.
    Auckland
    74
    3,357
    37
    They are fitted inside oil separator as a last stage of separation, larger vessels have access covers that lets your access them.
    Jul 2010
    Mombasa
    57
    52
    14
    Ok then these separators are welded type can not see inside unless cut open
  19. #19
    Mar 2006
    Merate (LC) - Italy
    2,549
    Baffles may be pulled or pushed from the inlet manifold, by using a hooked rod or by boroscopic inspection.
  20. #20
    Jul 2010
    Mombasa
    57
    52
    14
    Ok will check and see if can do the above and get back to you
  21. #21
    Jul 2010
    Mombasa
    57
    52
    14
    any one with any other suggestions
  22. #22
    Feb 2009
    india
    Replace oil filter built in compressor and charge 10 litre instead of 8 and check
  23. #23
    Feb 2009
    india
    Hi.
    if problem remain then recover refrigerant and cut oil sperator from bottom and check buffle
  24. #24
    Jul 2010
    Mombasa
    57
    52
    14
    ok thanks will try that and get back to you all
  25. #25
    Sep 2009
    Cyprus
    64
    110
    15
    Magoo are u working with FRICK and SABROE compressors?
  26. #26
    Nov 2009
    44
    9
    check oil level using 2x 1/4" hoses and a sight glass, how much oil did you drain? you should only put back what you have taken out. if oil plate charge is 8lts you should take into account the oil cooler! the min oil level from bottom of seperator is 150mm and max about 500mm. Check level 5mins after machine has stopped to allow oil level to settle. (sounds like not enough oil in sepator) GOOD LUCK.
  27. #27
    Jul 2010
    Mombasa
    57
    52
    14
    checked oil level above required oil level more than 500mm
  28. #28
    Auckland
    74
    3,357
    37
    Hi York man,
    generally work on Mycoms with re mote oil separators, vertical. But do as well work with Frick and Sabroe screw and recips.
    Meab.
    are you confusing an oil separator with a discharge muffler. Just a thought. Like I said earlier I do not know the machine. If a discharge muffler they can have baffle failures and make one hell of a noise.
  29. #29
    Oct 2009
    merida mexico
    54
    282
    15
    trane coalecentes not use filters, oil separators are sealed in the noise is really the separator or the compressor, as I said at the start if the oil supply line to the compressor is blocked causing the compressor is very noisy. ondensador Czech saturated temperature and oil temperature if less than 5 ° f the oil filter change, high oil temperature also causes the compressor is noisy
  30. #30
    Sep 2010
    Canada
    13
    Any other diagnostics on UCP2 controller?
    I agree with the previous poster. Restricted oil makes these compressors extremely noisy (the good thing is that they can take some abuse but don't try to pull them into a vacuum). Make sure the oil isolation valve on the supply side has come off the front seat.
    Look for a drawing of the oil internals for this compressor. It is possible the master oil solenoid is not picking up. Is it powered? Master oil solenoid will provide oil for rotor coat as well as bearings. Is it making adequate pressure (pumping)?
    You should be able to feel the hot oil start to come out of the oil separator in a short time after a cold start up.
  31. #31
    Jul 2010
    Mombasa
    57
    52
    14
    Magoo
    It is an oil separator and am not confusing for discarge Muffler
    BekTek
    Yes oil pumping oil temp ranges between 38 and 41 degrees centigrade
  32. #32
    May 2010
    singapore
    most likely is the oil separator baffles plate, i have come across a detached plate and it made a loud hammering noise......
  33. #33
    May 2006
    India
    74
    399
    could be excess oil in the separator which may be knocking in the separator ....?
  34. #34
    Aug 2001
    Gold Coast, Australia
    600
    28
    Could be. I have it in the back of my head that those separators can be picky about the oil level being within the limits. Unfortunately it's too long since I worked on them to remember.
    Hopefully one of the still-at-Trane guys'll be along soon.
  35. #35
    Jul 2010
    Mombasa
    57
    52
    14
    Hi Guys
    a thought has occured to me and decided to share and get your suggestions. could it be that the new oil we have just put into the system is too light and need to put in some heavy oil as is done in motor vehicles after a few years of use.
  36. #36
    Mar 2006
    Merate (LC) - Italy
    2,549
    Hi Guys
    No. Compressors aren't internal combustion engines. And even if they were, here the noise isn't coming from loose components by wear and tear, as far as we know.
  37. #37
    Jul 2010
    Mombasa
    57
    52
    14
    why can noise not be could be carried into the separator and we could be hearing it there
  38. #38
    Mar 2006
    Merate (LC) - Italy
    2,549
    I don't see the logic behind the concept "noise from separator = higher viscosity oil needed in the compressors". But if you do, go ahead.
    Some times the easiest way is the best way: "noise from separator = separator noisy".
  39. #39
    Aug 2001
    600
    28
    Which makes me wonder - is the oil in there the proper Trane oil? If it isn't, that may be part or all of the problem.
  40. #40
    Jul 2010
    Mombasa
    57
    52
    14
    Guys
    thanks to you all for your suggestion i pumped in little more oil level now at 600mm at 100mm more than required. Noise level reduced but now unit trips on oil system fault. Oil temp at 28deg centigrade ambient temp at 32 deg centi. Any suggestion and once again thanks for all your much appreciated advise.
  41. #41
    Mar 2006
    Merate (LC) - Italy
    2,549
    28°C oil temperature? Too cold and probably too thick. Still convinced that problem is a baffle.
  42. #42
    Jul 2010
    Mombasa
    57
    52
    14
    but noise now eliminated although you are right oil temp too low and mind you both heaters working
  43. #43
    Mar 2006
    Merate (LC) - Italy
    2,549
    The noise is gone because the oil is cold and thick and behaves like a hydrodynamic damper. Oil shall be in the range 60-90°C. You are probably experiencing liquid flashing off from oil or excessive and uncontrolled remote cooling, if any cooler is connected to the oil circuit.
  44. #44
    Oct 2009
    merida mexico
    54
    282
    15
    could expose the temperatures and pressures that will appear in the panel to see how the machine is operating
  45. #45
    Jul 2010
    Mombasa
    57
    52
    14
    The oil cooler is the design oil cooler on the top of the condensor
  46. #46
    Mar 2006
    Merate (LC) - Italy
    2,549
    So what? Can't it be wrong?
  47. #47
    Jun 2008
    TURKMENISTAN
    44
    14
    hi!
    i had the same problem with a train unit but model was different. is there any oil line under the evaporatr comming to the compressor? and when u mentioned the noise did u check the oil? i mean it was still in the oil separator or it was already goes to condenser? there is a service valve for oil near the sperator. when u open this valve oil is comming? i think no.
  48. #48
    Jul 2010
    Mombasa
    57
    52
    14
    No NickName i do not think the design could be wrong we have four chillers on the site and am sure not all can be wrong.
    hoodemar yes there is oil in the separator as checked with the 1/4" hoses and sight glass
  49. #49
    Mar 2006
    Merate (LC) - Italy
    2,549
    28°C oil temperature is wrong. If all of them are as cold as that, they are all wrong.
    That being said, I'm unsubscribing the thread.
  50. #50
    Jul 2010
    Mombasa
    57
    52
    14
    No i think you not understand me the rest of the chillers temp range between 45 to 55 degrees C it is only the unit that i topped up extra oil that has the low temp the low temp has been brought about by the additional oil that i put in to stop the noise
  1. Trane chiller problem
    By dannycool in forum Air Conditioning
    Last Post: 08-04-2010, 11:31 PM
  2. Trane chiller
    By Lman in forum Trouble Shooting
    Last Post: 13-11-2009, 03:51 PM
  3. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Last Post: 28-10-2009, 09:47 PM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Last Post: 06-10-2008, 03:23 PM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Last Post: 08-03-2007, 06:14 PM