    Re: Trane Chiller: Noisy Oil Separator



    Quote Originally Posted by meab View Post
    No NickName i do not think the design could be wrong we have four chillers on the site and am sure not all can be wrong.

    hoodemar yes there is oil in the separator as checked with the 1/4" hoses and sight glass
    at my problem, oil was completely going to the evaporator and there was a pipe 1/4" was comming from evap to compressor. also there is a small filter on this line. Oil filter was dirty and this small filter was dirty. so oil was not turning back to the separator and separotor was completely empty.

    ur situation is different, because u have oil in separator. is there any mesh? did u see anything in the drier filter? or in the oil filter?




  2. #52
    Join Date
    Oct 2009
    Location
    USA
    Age
    67
    Posts
    28
    Rep Power
    0

    Re: Trane Chiller: Noisy Oil Separator

    I use to work on these alot and trying to get my memory together, make sure all the service valves for oil flow are open. From memory if one service is closed it will restrict oil flow and cause the bearing to whine loud. When checking oil level, make sure all valves are open and there is no ***** pressure boiling off differential in the system. Let the oil level stablize in your ***** hose sight glass for 15 minutes. If you are for sure there is the right amount volume of oil, then my very last thought is the centrifugal baffles are loose.

  3. #53
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Thanks to all of you for your most valued suggestions

  4. #54
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane Chiller: Noisy Oil Separator

    Question:

    the machine's use to brine or comfort?

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Trane chiller problem
    By dannycool in forum Air Conditioning
    Replies: 6
    Last Post: 08-04-2010, 11:31 PM
  2. Trane chiller
    By Lman in forum Trouble Shooting
    Replies: 4
    Last Post: 13-11-2009, 03:51 PM
  3. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •