    Trane Chiller: Noisy Oil Separator



    Hi.

    Carried out an oil Change on a Trane TRA Screw compressor. Drained old oil Charged new oil 8 Ltrs as specified on Name Plate used Trane 025E oil as Specified and after starting the system the oil separator developed a new very loud whinning noise. What could be the cause of this. Please advise



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane Chiller: Noisy Oil Separator

    Quote Originally Posted by meab View Post
    Hi.

    Carried out an oil Change on a Trane TRA Screw compressor. Drained old oil Charged new oil 8 Ltrs as specified on Name Plate used Trane 025E oil as Specified and after starting the system the oil separator developed a new very loud whinning noise. What could be the cause of this. Please advise
    Hi does this noise continue when comp is loaded??
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Yes the noise does not stop have been running the unit with the noise

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane Chiller: Noisy Oil Separator

    reopen the valves of oil. which model of machine is it? Oil 8lts rtaa080 is a machine?

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    Two reasons:
    1) the oil heaters are touching together and vibrating when the compressor is running
    2) the internal baffles are coming loose and vibrating against the case.

    In the first case, you can try removing one or more heaters. In the other case, return the oil separator for repair.

  6. #6
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    All valves open unit running but noisy

  7. #7
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Oil Heaters OK. may need to check the baffles as per your advise thanks

  8. #8
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Unit Model No RTAB 212

  9. #9
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane Chiller: Noisy Oil Separator

    low flow of oil is causing the compressor is very noisy, recover the refrigerant and verify that no lines are blocked lubrication.

  10. #10
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Hi have tried all the above suggestions. Carried out an oil change to another system and again the same noise has resulted. Do not understand why this should happen

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    Did you inspect the baffles?

  12. #12
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Not yet checked baffles

    Although i am surprised would fresh oil effect the baffles in 2 machines,

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    No, you should have checked the baffles before changing the oil. No effect by fresh oil. My first suggestion was to check baffles (scroll back in the thread). I still guess the cause is related to badly welded baffles.

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Trane Chiller: Noisy Oil Separator

    Do not know the actual machine, but do they have coalessers fitted, sounds could be from that they have shifted or burst out and flapping around. Why, I would not know.

  15. #15
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    The Units are Trane Chillers Model TRTAB 212 with 2No. Screw Compressors Model CHHN060KEN070A.

    What are Coalessers? do not know these would they have another name?

  16. #16
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    Coalescer is the other name of the oil separator.

  17. #17
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Trane Chiller: Noisy Oil Separator

    They are fitted inside oil separator as a last stage of separation, larger vessels have access covers that lets your access them.

  18. #18
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Ok then these separators are welded type can not see inside unless cut open

  19. #19
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    Baffles may be pulled or pushed from the inlet manifold, by using a hooked rod or by boroscopic inspection.

  20. #20
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Ok will check and see if can do the above and get back to you

  21. #21
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    any one with any other suggestions

  22. #22
    Join Date
    Feb 2009
    Location
    india
    Posts
    17
    Rep Power
    0

    Re: Trane Chiller: Noisy Oil Separator

    Replace oil filter built in compressor and charge 10 litre instead of 8 and check

  23. #23
    Join Date
    Feb 2009
    Location
    india
    Posts
    17
    Rep Power
    0

    Re: Trane Chiller: Noisy Oil Separator

    Quote Originally Posted by meab View Post
    Hi.

    Carried out an oil Change on a Trane TRA Screw compressor. Drained old oil Charged new oil 8 Ltrs as specified on Name Plate used Trane 025E oil as Specified and after starting the system the oil separator developed a new very loud whinning noise. What could be the cause of this. Please advise
    if problem remain then recover refrigerant and cut oil sperator from bottom and check buffle

  24. #24
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    ok thanks will try that and get back to you all

  25. #25
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    64
    Posts
    110
    Rep Power
    15

    Re: Trane Chiller: Noisy Oil Separator

    Magoo are u working with FRICK and SABROE compressors?

  26. #26
    Join Date
    Nov 2009
    Location
    england
    Age
    44
    Posts
    9
    Rep Power
    0

    Re: Trane Chiller: Noisy Oil Separator

    check oil level using 2x 1/4" hoses and a sight glass, how much oil did you drain? you should only put back what you have taken out. if oil plate charge is 8lts you should take into account the oil cooler! the min oil level from bottom of seperator is 150mm and max about 500mm. Check level 5mins after machine has stopped to allow oil level to settle. (sounds like not enough oil in sepator) GOOD LUCK.

  27. #27
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    checked oil level above required oil level more than 500mm

  28. #28
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Trane Chiller: Noisy Oil Separator

    Hi York man,
    generally work on Mycoms with re mote oil separators, vertical. But do as well work with Frick and Sabroe screw and recips.

    Meab.
    are you confusing an oil separator with a discharge muffler. Just a thought. Like I said earlier I do not know the machine. If a discharge muffler they can have baffle failures and make one hell of a noise.

  29. #29
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane Chiller: Noisy Oil Separator

    trane coalecentes not use filters, oil separators are sealed in the noise is really the separator or the compressor, as I said at the start if the oil supply line to the compressor is blocked causing the compressor is very noisy. ondensador Czech saturated temperature and oil temperature if less than 5 ° f the oil filter change, high oil temperature also causes the compressor is noisy

  30. #30
    Join Date
    Sep 2010
    Location
    Canada
    Posts
    13
    Rep Power
    0

    Re: Trane Chiller: Noisy Oil Separator

    Any other diagnostics on UCP2 controller?
    I agree with the previous poster. Restricted oil makes these compressors extremely noisy (the good thing is that they can take some abuse but don't try to pull them into a vacuum). Make sure the oil isolation valve on the supply side has come off the front seat.
    Look for a drawing of the oil internals for this compressor. It is possible the master oil solenoid is not picking up. Is it powered? Master oil solenoid will provide oil for rotor coat as well as bearings. Is it making adequate pressure (pumping)?
    You should be able to feel the hot oil start to come out of the oil separator in a short time after a cold start up.

  31. #31
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Magoo

    It is an oil separator and am not confusing for discarge Muffler

    BekTek

    Yes oil pumping oil temp ranges between 38 and 41 degrees centigrade

    Thanks

  32. #32
    Join Date
    May 2010
    Location
    singapore
    Posts
    6
    Rep Power
    0

    Re: Trane Chiller: Noisy Oil Separator

    most likely is the oil separator baffles plate, i have come across a detached plate and it made a loud hammering noise......

  33. #33
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Trane Chiller: Noisy Oil Separator

    could be excess oil in the separator which may be knocking in the separator ....?

  34. #34
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane Chiller: Noisy Oil Separator

    Could be. I have it in the back of my head that those separators can be picky about the oil level being within the limits. Unfortunately it's too long since I worked on them to remember.
    Hopefully one of the still-at-Trane guys'll be along soon.

  35. #35
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Hi Guys

    a thought has occured to me and decided to share and get your suggestions. could it be that the new oil we have just put into the system is too light and need to put in some heavy oil as is done in motor vehicles after a few years of use.

  36. #36
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    Quote Originally Posted by meab View Post
    Hi Guys

    a thought has occured to me and decided to share and get your suggestions. could it be that the new oil we have just put into the system is too light and need to put in some heavy oil as is done in motor vehicles after a few years of use.
    No. Compressors aren't internal combustion engines. And even if they were, here the noise isn't coming from loose components by wear and tear, as far as we know.

  37. #37
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    why can noise not be could be carried into the separator and we could be hearing it there

  38. #38
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    I don't see the logic behind the concept "noise from separator = higher viscosity oil needed in the compressors". But if you do, go ahead.

    Some times the easiest way is the best way: "noise from separator = separator noisy".

  39. #39
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane Chiller: Noisy Oil Separator

    Which makes me wonder - is the oil in there the proper Trane oil? If it isn't, that may be part or all of the problem.

  40. #40
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    Guys
    thanks to you all for your suggestion i pumped in little more oil level now at 600mm at 100mm more than required. Noise level reduced but now unit trips on oil system fault. Oil temp at 28deg centigrade ambient temp at 32 deg centi. Any suggestion and once again thanks for all your much appreciated advise.

    Thanks

  41. #41
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    28°C oil temperature? Too cold and probably too thick. Still convinced that problem is a baffle.

  42. #42
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    but noise now eliminated although you are right oil temp too low and mind you both heaters working

  43. #43
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    The noise is gone because the oil is cold and thick and behaves like a hydrodynamic damper. Oil shall be in the range 60-90°C. You are probably experiencing liquid flashing off from oil or excessive and uncontrolled remote cooling, if any cooler is connected to the oil circuit.

  44. #44
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane Chiller: Noisy Oil Separator

    could expose the temperatures and pressures that will appear in the panel to see how the machine is operating

  45. #45
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    The oil cooler is the design oil cooler on the top of the condensor

  46. #46
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    Quote Originally Posted by meab View Post
    The oil cooler is the design oil cooler on the top of the condensor
    So what? Can't it be wrong?

  47. #47
    Join Date
    Jun 2008
    Location
    TURKMENISTAN
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: Trane Chiller: Noisy Oil Separator

    hi!
    i had the same problem with a train unit but model was different. is there any oil line under the evaporatr comming to the compressor? and when u mentioned the noise did u check the oil? i mean it was still in the oil separator or it was already goes to condenser? there is a service valve for oil near the sperator. when u open this valve oil is comming? i think no.

  48. #48
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    No NickName i do not think the design could be wrong we have four chillers on the site and am sure not all can be wrong.

    hoodemar yes there is oil in the separator as checked with the 1/4" hoses and sight glass

  49. #49
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Chiller: Noisy Oil Separator

    28°C oil temperature is wrong. If all of them are as cold as that, they are all wrong.
    That being said, I'm unsubscribing the thread.

  50. #50
    Join Date
    Jul 2010
    Location
    Mombasa
    Age
    57
    Posts
    52
    Rep Power
    14

    Re: Trane Chiller: Noisy Oil Separator

    No i think you not understand me the rest of the chillers temp range between 45 to 55 degrees C it is only the unit that i topped up extra oil that has the low temp the low temp has been brought about by the additional oil that i put in to stop the noise

Page 1 of 2 12 LastLast

Similar Threads

  1. Trane chiller problem
    By dannycool in forum Air Conditioning
    Replies: 6
    Last Post: 08-04-2010, 11:31 PM
  2. Trane chiller
    By Lman in forum Trouble Shooting
    Replies: 4
    Last Post: 13-11-2009, 03:51 PM
  3. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •