    trane RTAC alarm



    Hello to everybody.I have a problem with a trane rtac 155.
    It appears alarm 2E6.I know it is related with a clock.
    How can i fix it?Why it appeared?
    Can anybody help?



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,700
    Rep Power
    47

    Re: trane RTAC alarm

    Hi Harry.
    The official answer is below, It sounds a bit Heavy!!
    Grizzly


    2E6 Check Clock Info Latch The real time clock had detected loss of its oscillator at some time in the past. This diagnostic can be effectively cleared only by writing a new value to the chiller's time clock using the TechView or DynaView's "set chiller time" functions. Remote

  3. #3
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: trane RTAC alarm

    Thanks grizzly.What problem can this clock create to the unit?
    Any other way to reset this?I have a problem with tech view.I cannot connect.I have the message[ connection failed].

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: trane RTAC alarm

    Quote Originally Posted by HARRY 7 View Post
    Thanks grizzly.What problem can this clock create to the unit?
    Any other way to reset this?I have a problem with tech view.I cannot connect.I have the message[ connection failed].
    Hi sounds like a bad com setting
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: trane RTAC alarm

    Hi goshen.Does this alarm affects the chiller??

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: trane RTAC alarm

    clock is a non latching alarm.
    what version techview do you use?
    do you connect straight from a serial port or through a USB-RS232 adapter?
    If it ain't broke, don't fix it!

  7. #7
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: trane RTAC alarm

    It is version 12.1.
    I connect through a USB-RS232 adapter.
    I have the same connection problem to a chiller RTAC 350.

  8. #8
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: trane RTAC alarm

    make sure u have the com port set up to the right one. V12.1 is compatable with higher com ports than 3.
    If it ain't broke, don't fix it!

  9. #9
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: trane RTAC alarm

    Thanks low rider.I will check it the next time i will go.

  10. #10
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: trane RTAC alarm

    Hi Harry,
    The latest software is 12.1 and SP4.
    Trane control department in France has tested 3 USB à RS232 adaptors. One of them is IOGEAR GUC232A.
    I have it but I also bought a used laptop with serial port only to use it in TechView, so I have not test it yet.
    2E6: Easy view boards have a battery for the clock. I have several times change the battery but the problem came out again.
    The problem is a specific failure on the board. I always change the board with a Dynaview.
    2E6 is not critical for the operation of the chiller, but you always have an alarm. If this is not a problem it’s OK.
    Hope I help.

  11. #11
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: trane RTAC alarm

    Thanks Geardrive for your information.

  12. #12
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: trane RTAC alarm

    Are you located in Athens?

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. trane rtac 250 oil filter replacment
    By anish in forum Trouble Shooting
    Replies: 13
    Last Post: 29-01-2011, 02:14 PM
  3. Trane RTAC 170 , Phase reversal trip?
    By THE WOMBAT in forum Commercial
    Replies: 26
    Last Post: 09-07-2010, 01:23 AM
  4. Replies: 3
    Last Post: 13-06-2009, 01:39 PM
  5. trane rtac 275
    By anish in forum Air Conditioning
    Replies: 6
    Last Post: 01-10-2008, 10:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •