    HI

    i have a problem booting the Frick Quantum LX compressor control panel , the powering up sequence continues to repeat without displaying the operating status screen !!!

    please can anyone help me with this ??



  2. #2
    Join Date
    Oct 2007
    Location
    New Zealand
    Age
    51
    Posts
    52
    Rep Power
    17

    Re: Quantum LX booting problem

    You have a corrupt flash card. Remove the CF card and re-boot. It will start in the older Quantum screen. You can actually plug in a mouse and keyboard on the PS2 port to control if necessary.

  3. #3
    quantum's Avatar
    quantum Guest

    Re: Quantum LX booting problem

    Thanx for replying, but what should i do with the corrupted flash card ! should i replace it with a new one with a new software so as to get back the new quantum screen ?

  4. #4
    Join Date
    Oct 2007
    Location
    New Zealand
    Age
    51
    Posts
    52
    Rep Power
    17

    Re: Quantum LX booting problem

    Quote Originally Posted by quantum View Post
    Thanx for replying, but what should i do with the corrupted flash card ! should i replace it with a new one with a new software so as to get back the new quantum screen ?
    The corrupt ones are junk. Bin it? Or maybe re format and use it in your camera?
    Did you boot with the card out? This should prove there is not a hardware issue if it boots up in the the old Quantum display.
    If so you can get a new card from JCI. Did you save the setpoints (Software Maintenance) to a USB? Hope so or you will need to re-install all your operational parameters, also newer versions often have a few little changes and parameters you may need to check.

  5. #5
    Join Date
    Feb 2008
    Location
    TURKEY
    Age
    62
    Posts
    14
    Rep Power
    0

    Re: Quantum LX booting problem

    It just happened teh to us. The problem was a faulty program flash card. To check it you have to remove the flash card and see if program returns to a earlier version

Similar Threads

  1. MFI AMP6855 defrost problem
    By gliderpilot47 in forum Domestic
    Replies: 4
    Last Post: 12-01-2011, 12:11 PM
  2. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  3. Fujitsu Multi problem
    By BMS1 in forum Heat Pumps
    Replies: 15
    Last Post: 02-09-2010, 06:41 AM
  4. problem with GE air con power problem
    By Richie101 in forum Air Conditioning
    Replies: 6
    Last Post: 05-11-2009, 04:00 PM
  5. Hot start problem on VRV REYQ14M7W1B
    By cool#9 in forum Air Conditioning
    Replies: 9
    Last Post: 20-04-2007, 08:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •