    Hi Guys,
    I want to consider of using a desuperheater on return icewater to optimise the current install.
    When we reach temperatures of 40°C on the roof, the unit go's in overheating alarm on the condensor and stops. It takes about 4hrs to regain the desired roomtemperature. Keep in mind that is is for a cleanroom, and the workers there are in special suites and covered from head to tows.
    Is there anyone ho has already done something like this, and is it word doing?
    I am looking for some pro's and contra's. All hints are welcome.
    Ice
    11,024
    Re: de-superheater
    Water mister on the coil for times of high temperature perhaps.
    Jul 2009
    Brisbane
    67
    79
    15
    Re: de-superheater
    Add a secondary condenser for high ambient conditions with a 3 way split condenser valve. Or just fit a larger condenser with fan speed control
    May 2008
    66
    802
    Re: de-superheater
    this condensor already has fanspeedcontrol, it has 6 fans of 645mm diam. they are spraying water over it to cool it down, but it is not effective enough. also the cost of a worker that is standing thare playing whit a waterhose is not wat they want for the future hot days to come.
    Ice
    Aug 2009
    New Zealand
    2,554
    26
    Re: de-superheater
    Quote Originally Posted by icecube51 View Post
    Ice
    Gday Ice, go down to your hardware store, buy some little irrigation mister nossles the finest mist possible. (like you use at home in your garden). a water sloenoid and thermostat. the nossles should be set approx 600mm from the front of the air inlet to the condenser. Giving time for the water mist to evaporate in the air stream. This is cheap and very reliable. (it not the amount of water that is required but the anount of water that evaporates)
    The guy with hose is only spraying water on to the condenser in one place at any one time, so is not getting the true benefit of evapoative cooling
    Set your thermostat up with the sol valve at the just below your problem temperatures.
    May 2008
    66
    802
    Re: de-superheater
    I am afrayd that the condensor will soke itself full whit water and the result will be wors than whitout the water.
    Ice
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: de-superheater
    Ice
    I'm afraid you don't have a rough idea what you are talking about. As such, either you listen to the advice given, or kiss my compressor goodbye
    3,853
    Re: de-superheater
    Icecube, I think this is the type of system being talked about,
    http://www.microcool.com/cooling/precooling.shtml
    The mist is so fine as to evaporate before it reaches the condenser.
    Jon
    Aug 2009
    New Zealand
    2,554
    26
    Re: de-superheater
    Ice
    Each mister nossle (cheap ones) uses 8 litres per hour and normally has a mist pattern of 1m2 at 600mm, So you may need 6-8 nossles. This is less water than a good down pour of rain. Or you could go and buy a genuine mister system as MS posted.
    May 2008
    66
    802
    Re: de-superheater
    Jon
    Thanks monkey spanners, that is in fact a good idea.
    I will take a closer look, but it seams fine already. thanks for the tech-specs mad-fridgie, when considdering your wright, it is less than rain.