    de-superheater



    Hi Guys,

    I want to consider of using a desuperheater on return icewater to optimise the current install.
    When we reach temperatures of 40°C on the roof, the unit go's in overheating alarm on the condensor and stops. It takes about 4hrs to regain the desired roomtemperature. Keep in mind that is is for a cleanroom, and the workers there are in special suites and covered from head to tows.

    Is there anyone ho has already done something like this, and is it word doing?
    I am looking for some pro's and contra's. All hints are welcome.

    Ice



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: de-superheater

    Water mister on the coil for times of high temperature perhaps.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: de-superheater

    Add a secondary condenser for high ambient conditions with a 3 way split condenser valve. Or just fit a larger condenser with fan speed control

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: de-superheater

    this condensor already has fanspeedcontrol, it has 6 fans of 645mm diam. they are spraying water over it to cool it down, but it is not effective enough. also the cost of a worker that is standing thare playing whit a waterhose is not wat they want for the future hot days to come.

    Ice

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: de-superheater

    Quote Originally Posted by icecube51 View Post
    this condensor already has fanspeedcontrol, it has 6 fans of 645mm diam. they are spraying water over it to cool it down, but it is not effective enough. also the cost of a worker that is standing thare playing whit a waterhose is not wat they want for the future hot days to come.

    Ice
    Gday Ice, go down to your hardware store, buy some little irrigation mister nossles the finest mist possible. (like you use at home in your garden). a water sloenoid and thermostat. the nossles should be set approx 600mm from the front of the air inlet to the condenser. Giving time for the water mist to evaporate in the air stream. This is cheap and very reliable. (it not the amount of water that is required but the anount of water that evaporates)
    The guy with hose is only spraying water on to the condenser in one place at any one time, so is not getting the true benefit of evapoative cooling
    Set your thermostat up with the sol valve at the just below your problem temperatures.
    Last edited by mad fridgie; 15-07-2010 at 05:03 AM.

  6. #6
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: de-superheater

    I am afrayd that the condensor will soke itself full whit water and the result will be wors than whitout the water.

    Ice

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: de-superheater

    Quote Originally Posted by icecube51 View Post
    I am afrayd that the condensor will soke itself full whit water and the result will be wors than whitout the water.

    Ice
    I'm afraid you don't have a rough idea what you are talking about. As such, either you listen to the advice given, or kiss my compressor goodbye

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: de-superheater

    Icecube, I think this is the type of system being talked about,

    http://www.microcool.com/cooling/precooling.shtml


    The mist is so fine as to evaporate before it reaches the condenser.

    Jon

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: de-superheater

    Quote Originally Posted by icecube51 View Post
    I am afrayd that the condensor will soke itself full whit water and the result will be wors than whitout the water.

    Ice
    Each mister nossle (cheap ones) uses 8 litres per hour and normally has a mist pattern of 1m2 at 600mm, So you may need 6-8 nossles. This is less water than a good down pour of rain. Or you could go and buy a genuine mister system as MS posted.

  10. #10
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: de-superheater

    Quote Originally Posted by monkey spanners View Post
    Icecube, I think this is the type of system being talked about,

    http://www.microcool.com/cooling/precooling.shtml


    The mist is so fine as to evaporate before it reaches the condenser.

    Jon
    Thanks monkey spanners, that is in fact a good idea.
    I will take a closer look, but it seams fine already. thanks for the tech-specs mad-fridgie, when considdering your wright, it is less than rain.

    Ice
    Last edited by icecube51; 16-07-2010 at 04:17 PM.