    replacing daikin board



    can someone pleasehelp with the instruction for a main board for a daikin condensing unit m/n rxymq36mvju . need to replace the board already have new board.



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: replacing daikin board

    Swap the board like for like (1 terminal off 1 terminal on)Follow the instructions that come with the board to make any changes DONT set as the original

  3. #3
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: replacing daikin board

    I would just rip all the plugs out disconnect all wires and then just start putting back together. All the plugs are colour coded and mated so it is hard to get them wrong. Wires you can look at the diagram.
    Dont know that model because it is not sold in Aust

    Important notes

    If the PCB contains power transitors or diode bridges that require heat thermal past then put it back on.
    If there is repair info with the PCB read it because you may need to set the capacity dip switches or use a capacity adaptor based on the capacity of the unit.

    Got me interested in that model may just have to look up the specs

  4. #4
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: replacing daikin board

    WhichPCB this unit has 3 .

    If it is the controll PCB you should have received the repair in for the dip switches (B72A398D) unless you have a substitute part.

    If you get a U3 fault you will need to put the unit through test operation. Hold down the BS 4 button on the outdoor PCB for 5 seconds.

    Most info is found on the outdoor cover.

    Cheers

  5. #5
    ducunuwidmeat's Avatar
    ducunuwidmeat Guest

    Re: replacing daikin board

    its the main pc board . the only instruction that comes with the board is for the dip switches. now after setting the dip switche is there other instuction for commisioning the board?

  6. #6
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: replacing daikin board

    Not really. The basic setting should be o.k for what you want.
    Just set switches and turn power on.
    You will more than likely need to put it through a test operation.
    If it come up with U3 turn the indoor unit off at the controller and hold down the BS4 button on the outdoor PCB for 5 seconds. The controller will show test until the test function has finished.

    Only other settings would be setting mode 2 on the outdoor PCB which you shouldn't have too change.

    Thats all you should have to do.
    Put covers on while running test operation if air is able to bypass coil with covers off.
    No longer Active

  7. #7
    ducunuwidmeat's Avatar
    ducunuwidmeat Guest

    Re: replacing daikin board

    thanks . i got a hold of the distributor which sold me the board regarding the instruction. they have daikin tech called me. one tech said the dip switches labelled ds1 all switches should be the off position and dip switch labelled ds2 number 1 switch should be on and the balance remain off.he also stated that the new board need to be conditioned and i need instruction. the other tech stated thatdip switch labelled ds1 number 4 dip switch to on and the rest to remain in the off position. switch labelled ds2 number 1 to the on position and remaining to the off position. and he said no instruction needed. cannot get a hold of these guys. i noticed you said possibility will need to set mode 2 whats this? is there some type of instruction to set mode 2 ? thanks for any feed back.

  8. #8
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: replacing daikin board

    I am not 100% familiar with this unit because we don't have it in Aust however it looks like it share the same parts as our models. Setting mode 2 is a field code setting function that can be done on the outdoor PCB to change settings and operating parameters.
    Factory settings are fine . Outdoor cover should have information on this however if you are not familiar what they do then best not to play with them. No need to change.
    No longer Active

  9. #9
    ducunuwidmeat's Avatar
    ducunuwidmeat Guest

    Re: replacing daikin board

    thanks for all yor help i set dip switches to the settings per second tech from daikin. the only problem i had was code u3 . there was a large exhaust fan that was runninig approx 5 ft from condensing unit. i decide to turn exhaust fan and and ran test on unit again no problem. turned on exhaust fan and ran unit now working like a champ. again thanks for your help.

  10. #10
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: replacing daikin board

    No worries good to see you got it sorted
    No longer Active

Similar Threads

  1. Daikin new PCB board
    By ronaldo9 in forum Air Conditioning
    Replies: 5
    Last Post: 18-06-2009, 11:35 PM
  2. Daikin RZP1450V1 Main Board
    By Lumpy2 in forum Trouble Shooting
    Replies: 1
    Last Post: 03-06-2009, 09:59 PM
  3. Daikin Inverter board failures
    By Greengrocer in forum Air Conditioning
    Replies: 10
    Last Post: 21-05-2009, 04:35 PM
  4. Daikin Inverter Board / Compressor issues
    By Greengrocer in forum Air Conditioning
    Replies: 12
    Last Post: 21-04-2009, 10:12 PM
  5. Daikin VRV wiring adapter board
    By mchild in forum Air Conditioning
    Replies: 6
    Last Post: 24-11-2008, 11:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •