    Unhappy Weak portable cooler output



    I have Ariagel Eco 2000 R407C portable airconditioner (around 6000 Btu). The ouput air temperature is not very cool. Only 17 degrees C (approx 63 F). The outgoing air is very hot. I can't get any indications when searching leaks with a leak detector and I believe that these portable coolers leak seldomly. Any suggestions? The filter is OK and the machine isn't very dusty either.



  2. #2
    adam_brooks's Avatar
    adam_brooks Guest

    Re: Weak portable cooler output

    could be a crook expansion device causing drop in cooling performance and lower suction pressures also would cause it to make too much heat/ high pressures.

  3. #3
    Join Date
    Jul 2009
    Location
    Finland
    Age
    70
    Posts
    12
    Rep Power
    0

    Re: Weak portable cooler output

    Sounds possible. I measured the current draw and it is 3.5 A which is OK. So the compressor probably is in condition and can produce compression.

    Is there anything what I could do? I can't post pictures yet but please copypaste the address below and take a look. Is the red framed component the expansion device/valve? Sorry about stupid question. I am an electronic maintenance engineer.

    dy.fi/50r

  4. #4
    Join Date
    Aug 2008
    Location
    ireland
    Age
    48
    Posts
    12
    Rep Power
    0

    Re: Weak portable cooler output

    NO its the drier ,the one to the left coiled up in the black square cover is the exp device ,you could check temp difference on pencil drier,you have mark should be almost the same in and out 8-)

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Weak portable cooler output

    What state is the condenser coil in? Has it been cleaned?

    Is it a water cooled condenser?, been descaled?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Weak portable cooler output

    A 7000 btu a/c will use a capillary tube in place of a tx valve.What we need to know is the temp. difference across the evaporator,( air on and air off) which should be around 12 to 14 deg. c in a good working unit on medium fan speed. therefore with 17c coming out, i would expect say 29c air temp in the room, meaning a/c is fine just too small for the job.

Similar Threads

  1. Gas charge for portable beer cooler?
    By tom the blade in forum Technical Speculations
    Replies: 5
    Last Post: 11-09-2009, 09:07 AM
  2. Fabrication of Cooler Tube & Shell Cooler
    By rickyccong in forum Technical Discussions
    Replies: 1
    Last Post: 27-07-2009, 02:25 PM
  3. Cannot get the cooler to temp
    By coolrunnings1 in forum Fundamentals
    Replies: 13
    Last Post: 27-06-2009, 07:51 PM
  4. Air cooler broken
    By Rio69 in forum Trouble Shooting
    Replies: 5
    Last Post: 26-06-2009, 02:47 PM
  5. Got -80C portable 25L cooler?
    By scrapen in forum New Technologies
    Replies: 0
    Last Post: 11-04-2008, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •